- Reaction score
- 17,020
One of my neighbours asked me to price a supply out to a sauna they are putting in their garden. Wants it done by the 16th when its getting delivered, and im on holiday for a week... So this is my job for the 15th when I come back. Not had time to get BBB out and do the calcs,
4 - 5 Person Outdoor Traditional Sauna With 8kW Stove - https://www.uk-saunas.co.uk/traditional-saunas/4-5-person-outdoor-traditional-sauna-with-8kw-stove-eao-106.html
This is what they are getting.
Link says its 8kW, but tech specs state its 9kW... so no bigger than a shower. So i'm looking at a 40A load..... SWA cable, clipped direct from DB through utility room to outside. Short length buried under pathway, then clipped along garden wall to sauna position, approx. 20 m from DB to IP isolator at sauna.
Top of my head, 6mm...… Seems a little small.
Anyone know if I need to take diversity into account?
4 - 5 Person Outdoor Traditional Sauna With 8kW Stove - https://www.uk-saunas.co.uk/traditional-saunas/4-5-person-outdoor-traditional-sauna-with-8kw-stove-eao-106.html
This is what they are getting.
Link says its 8kW, but tech specs state its 9kW... so no bigger than a shower. So i'm looking at a 40A load..... SWA cable, clipped direct from DB through utility room to outside. Short length buried under pathway, then clipped along garden wall to sauna position, approx. 20 m from DB to IP isolator at sauna.
Top of my head, 6mm...… Seems a little small.
Anyone know if I need to take diversity into account?