Hi fellas,

Anyone any experience of wiring the biomass boiler in the following link? ETA Heiztechnik GmbH - ETA PC 20, 25 and 32 kW

I've wired loads of standard S Plan, Y plan, multi zone anf UFH systems but never a biomass.

The existing gas boiler system has two heating zone valves and a dhw zone valve.

I've taken a three channel programmer and all the gear expecting to wire up a S plan plus however the plumber says the programmer is not needed as all the controls are integrated into the biomass boiler.

Any help would be appreciated as I cant make any sense of the intructions.

Thank you
 
It depends how the job has been designed .
have connected most systems which keep the existing valves and programmer in place . switched live fires the pump which drains the boilers internal buffer tank , the boiler fires to keep the buffer tank at a specified temperature .

The boiler may need a switched live itself but who knows there is no wiring diagram in that link .
 
Depends what you want, The ETA boiler does indeed have all the controls you need. And are far more sophistatced and offer better control (including full web based remote as standard) than a standard controller.

It also includes the appropriate temperature probes - DHW cylinder etc.

If you havenlt attended the installation course, don't touch it, else the efficiency of the boiler will mean that you could be consuming twice as much fuel as you need.

Does it have a buffer tank?
 

Reply to Biomass ETA pc 20-32kw in the Solar Thermal Advice Forum area at ElectriciansForums.net

Similar Threads

Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
469
Hi, I’m not an electrician or a plumber, but I am confident diyer and am not completely incompetent! I have a new build house with a boiler/hot...
Replies
13
Views
4K
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock