I was testing brand new static caravan other day which came to the park recently. I had to test before it goes for hire or sale. I got Ze reading at caravan CU is 130 ohms and same as out side pitch bollard or hook point as well. Earthing system around the park is TNS. Hook up point is fed with two core SWA and steel wire has been used as earth. Inside caravan installation is sound but when you do live test all Zs readings will be well to high or doesn't comply with Regs. Now I am stuck to provide EICR for that caravan as satisfactory or unsatisfactory. Please anyone can advice me. Many Thanks.
 
sounds like the site earthing system has a problem. 130ohms on TN-S is a silly figure. check the Ze at source. if that is below 0.8ohms, then there is a problem with the cabling to the hook-up points.
 
and how is the swa ARMOUR glanded/terminated. a couple of strands in a choc block is favourite on caravan sites.
 
From what I can gather you are testing the caravan as opposed to the pitch. Therefore it would be a tad harsh to code the caravan installation as it will only be as good as the supply it is connected to.
 
From what I can gather you are testing the caravan as opposed to the pitch. Therefore it would be a tad harsh to code the caravan installation as it will only be as good as the supply it is connected to.

I suppose you could give the caravan all the dead tests and provisionally pass it but it would still fail and EICR C2 as its connected to and forms part of a dodgy installation.
 
Yes but it's not the van installation that is at fault. Op can it not be moved to another pitch?
 
Check the swa is properly glanded etc.

Last static I looked at swa into supply box no glands armoured all cut short of box, although was 16mm earth.

TT system ZE was 21.6 ohms
 

Reply to bks in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
Hi, I've got to a point where I need to complete the EIC for the caravan I've been working on. This isn't a static caravan, so will be going from...
Replies
2
Views
1K
Hi all, Just a electrical student here, and on holiday at a caravan park so, of course, i go snooping about a bit for the electrics. I notice...
Replies
18
Views
4K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock