Our company policy is to test each joint. His method won't show up any individual high joints.
 
Modern Ductor tester, takes 10s for each test. All stored internally and can be downloaded to PC. Compared to the amount of faffing about making shorts, calculation and repositioning the shorts, I know what I would be doing. The only issue I ever found with busbars was over-torque, construction guys had been at it with their big-boy spanners and tightened the sections too much causing high resistance. Had to go back, loosen them all and have them redone to the right torque.

We have Fluke Battery testers, that you can test the cell resistance and internal impedance on a each cell in a 120 cell battery in literally 5 minutes. Hook it up to a PC an you can instatly identify any weak cells.
 
The ductor tester we have doesn't store the readings that is the next model up from ours. Not too much hassle to be honest.

I use a celltron battery analyser, sounds similar to your fluke. Tests each cell, readings in mhos and tells you whether it is good or not and you can identify deterioration and change out before they fail.
 
Do you have the resistance of the installed bus bars,manufacturer will give their measurements.
Then at least you have a reference point,to check your resistances.
Also if possible voltage test at prone areas.
 
my double decker bus was 30ft. long and had a bar in it.
 

Reply to Busbar Ductor Testing in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi Guys After bit of advice please as we don't do much data normally, tend to sub it out. Had garden building this week which we'd run in SWA...
Replies
9
Views
425
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
693
Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
Replies
38
Views
4K
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
748

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock