Search the forum,

Discuss Cable tray or basket for Domestic install in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
HI
I am thinking of using steel cable tray or or basket with a cover for a vertical in a domestic garage to the consumer unit. I am looking at this solution because clipping to wall is no longer particularly viable due to number of cables and the damage past clips have already done to the wall plus the cables could be damaged as they are in the garage/ workshop.

Trunking would be neat but I am aware that some circuits are quite heavily loaded,
one ring for kitchen and utility,
large induction cooker,
immersion (not used very often but theoretically significant)
and likely at least one EV charger in the next couple of years I need to be aware of cable grouping factors.

Trunking would be ok at the moment but I feel that once EV charging is added to the equation some ventilation would be very useful.

I am thinking along the lines that perforated cable trays or baskets would be a good solution. It's possible to buy plastic cable tray with covers but that's quite expensive. I was looking at metal cable trays but covers don't appear to be available, maybe when a cover is required another tray is turned upside down and put on top? if this is the solution whats the best way to secure it?

I can see cable baskets come with covers, any reason I can't use baskets on a vertical run secured to a wall?

By the way are there any books or web sites you can recommend that cover cable management installation in detail. Things like on site guides, BS7671, guidance notes don't appear to cover this area in much detail.

Thanks
 
HI
I am thinking of using steel cable tray or or basket with a cover for a vertical in a domestic garage to the consumer unit. I am looking at this solution because clipping to wall is no longer particularly viable due to number of cables and the damage past clips have already done to the wall plus the cables could be damaged as they are in the garage/ workshop.

Trunking would be neat but I am aware that some circuits are quite heavily loaded,
one ring for kitchen and utility,
large induction cooker,
immersion (not used very often but theoretically significant)
and likely at least one EV charger in the next couple of years I need to be aware of cable grouping factors.

Trunking would be ok at the moment but I feel that once EV charging is added to the equation some ventilation would be very useful.

I am thinking along the lines that perforated cable trays or baskets would be a good solution. It's possible to buy plastic cable tray with covers but that's quite expensive. I was looking at metal cable trays but covers don't appear to be available, maybe when a cover is required another tray is turned upside down and put on top? if this is the solution whats the best way to secure it?

I can see cable baskets come with covers, any reason I can't use baskets on a vertical run secured to a wall?

By the way are there any books or web sites you can recommend that cover cable management installation in detail. Things like on site guides, BS7671, guidance notes don't appear to cover this area in much detail.

Thanks
What cable type will you be using?
 
TBH I wouldn't worry too much about grouping factors in this instance. If you look at the expected usage of the circuits I doubt very much they'll be at any significant load together at any time, have a feel and see how hot the cables are at the minute under normal load conditions.
 
I've thrown long runs of basket into premium domestic new-builds before where there's been lots of lighting radials and data-comms to contend with. If it's a vertical run, wouldn't tray be quicker and cheaper?
 

Reply to Cable tray or basket for Domestic install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This might come across as a really daft question to people who work with cable tray quite often but as part of my AM2, I am to clip FP200 to the...
Replies
31
Views
2K
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
721
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
301
Hi, I have two questions about domestic wiring In Ireland 1. Should conduit be used when passing multiple T&E cables (2.5mm) through a garage...
Replies
6
Views
869
I have some PECSO HO7RN-F 3G1.5 Flex cable that i want to use to wire up some outside LED security lights that are 240v. The cable will be clipped...
Replies
1
Views
588

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock