Discuss Can i hardwire a plug and play AEG induction hob? in the DIY Electrical Advice area at ElectriciansForums.net

Malpin77

DIY
Reaction score
5
We've recently brought a new build house and it's come with an AEG induction hob. We quickly realised there wasn't enough power to heat more than 2 pans at once. Rather pointless given its a 4 ring hob and slightly challenging cooking xmas dinner!

We've had Bellway out and they explained its a plug and play so there's only 13amp power supplying it. We would need to purchase a new hob and then hardwire it instead so there's enough power to use all 4 hobs.

What weve since realised is that there's already a separate circuit for the hob which is running at the 30amp required for hardwiring. This may be a stupid question but could I simply cut the plug off our current hob, remove the socket then hardwire it? This should provide the extra power needed.

I'd rather not spend out another ÂŁ300 on a new hob if it's not required. My concern is the plug and play hob isn't capable of dealing with the extra power so at the same time don't want to bust the current hob.

If useful the model is

AEG HK604200IB 59cm Induction Hob​

Any help would be much appreciated. Over the past few days I've been searching online and in the manual but struggling to find anything on the topic.

Thanks all
 
What happens you you try to heat with all four rings.

Edit. Just been looking at these plug and play hobs as I have never heard of them. It seems they restrict the power output so a 13A plug can be fitted making it easy for the end user to install. Altering its means of connection from a 13A plug to being hard wired will make no difference. Unless someone is more savvy with these appliances I believe your only option is an alternative hob.
 
Last edited:
According to the user manual, you can use any combination of heating zones but they will operate at a reduced power output if the total load exceeds 13A.

You should not remove the plug and connect it directly as the fuse is part of the electrical protection of the appliance. Doing so will give you no benefit as the manual appears to state a maximum power demand of 3kW (i.e. the hob is designed to limit itself).

If I was in your position, I might be inclined to check the sale particulars, but I suspect they have supplied exactly what you agreed and in this case it's down to the fact that you've misunderstood the capabilities of the hob. If however it doesn't reduce the power and allow you to use all four zones, that may be a fault that should be looked at under warranty (assuming it's still under warranty).
 
Hi - as per @SparkyChick - it’s got 6.5kW of elements but it’s controller manages this so the max load is 3kW. The unit is factory supplied with a 13A plug. Reading the manual just now I could not see a user function to disable the power controller. And there’s no point making any cable changes if the power controller can’t be disabled. AEG may be able to assist in some secret manufacturers way, but I suspect they’ll just suggest you replace the hob, sorry.
 
Thanks all for your replies, really helpful. It's not the answer I was hoping for but I now know I need to suck it up and buy a new hob!

Joining this forum was just a shot in the dark before just making a call on what to do. I didn't expect such quick responses. Thanks again for all your time looking at this.
 

Reply to Can i hardwire a plug and play AEG induction hob? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
Hello, two parts here....please forgive any incorrect terminology used! I am looking to replace my gas hob with an induction hob (this one...
Replies
1
Views
2K
hello, we have recently brought a new build house and we want to upgrade our gas hob for an induction hob, we have already brought the hob which...
Replies
21
Views
4K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Last night I was cooking dinner on my induction hob. While I had my back turned to the hob I heard a lot of crackling and popping and then smoke...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock