Discuss Can you ‘N/A’ most of a Minor Works for a like for like replacement? in the UK Electrical Forum area at ElectriciansForums.net

Weezy

-
Reaction score
64
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a minor works certificate.

Came into the office today to find they now want minor works certificates for about 250 fans we replaced.

Now normally if you was just doing a like for like swap no one would start checking the water/oil bonding, and recording circuit details or even looking to see what system of earth the property has, therefore my question is “since these items havnt been inspected would i be complying by simply marking most of the certificate as N/A?”

There’s simply no way we’re going to re visit 250 propertys some up to 45 miles away just to tick a box on a form that technically doesn't even need issuing for a double insulated fan swap over. i don’t want to get into a debate if it’s ethically right or wrong i just want to make sure im complying.

How iv always interpreted it was you may “n/a” something not inspected and my reasoning for not inspecting bonding would be because a replacement doesn’t require you to, therefore it must be okay to record bonding on a minor works as n/a. Do people agree?
 
NA for bonding would be for if there wasn't any and it wasn't required.
NV for couldn't / didn't need to verify.
 
Sounds like it's going to be a waste of paper as well as time...but if that's what's required.
Personally, I would contact the council department in question and have a discussion with whoever holds sway.
As previous, if you provide certificates, N/V.
250 certs at 5 minutes each, even, would be a long pain.
and a lot of N/V's.
 
Sounds like it's going to be a waste of paper as well as time...but if that's what's required.
Personally, I would contact the council department in question and have a discussion with whoever holds sway.
As previous, if you provide certificates, N/V.
250 certs at 5 minutes each, even, would be a long pain.
and a lot of N/V's.
If it’s an option and they use nic online the cert could be copied with the results that you wanted to be the same automatically filled out after the first one
 
Sounds like it's going to be a waste of paper as well as time...but if that's what's required.
Personally, I would contact the council department in question and have a discussion with whoever holds sway.
As previous, if you provide certificates, N/V.
250 certs at 5 minutes each, even, would be a long pain.
and a lot of N/V's.
Well it is applicable you just didn't verify it.
NA for bonding would be for if there wasn't any and it wasn't required.
NV for couldn't / didn't need to verify.
What i’m getting at is if fill out 250 forms with “N/V” for a large portion of it i’m technically correct in doing so?

I agree it’s a complete waste of paper and time but if they insist we have to do it we wanna be able to do it as quickly as possible but also correctly to cover myself incase they say “you’ve put NV for a lot of this” i can say “well it wasn’t verified because it was just a replacement and therefore we didn’t have to”

Im just making sure im correct in saying this, id hate to fill out 250 forms and then have to fill out another 250… The sad thing is in reality we all know no one’s even gonna look at them.
 
Always a difficult one this, if the client asked before the works were completed then that’s fine, costs added to the works.
It’s a lot of works not to be certified..
Checking the MPBC’s are in place can be difficult so that could be marked by a limitation, & ask for any Certification document if available for you. I’d usually do the basic Zs…Rcd…OCPD etc
But if the Client didn’t ask for MWC then costs should be directed back at them
 
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a minor works certificate.

Came into the office today to find they now want minor works certificates for about 250 fans we replaced.

Now normally if you was just doing a like for like swap no one would start checking the water/oil bonding, and recording circuit details or even looking to see what system of earth the property has, therefore my question is “since these items havnt been inspected would i be complying by simply marking most of the certificate as N/A?”

There’s simply no way we’re going to re visit 250 propertys some up to 45 miles away just to tick a box on a form that technically doesn't even need issuing for a double insulated fan swap over. i don’t want to get into a debate if it’s ethically right or wrong i just want to make sure im complying.

How iv always interpreted it was you may “n/a” something not inspected and my reasoning for not inspecting bonding would be because a replacement doesn’t require you to, therefore it must be okay to record bonding on a minor works as n/a. Do people agree?
I would 100% have insisted on this in writing. I may even have added that if you decide you want want certificates then there will be an extra cost. I write so bloody much now in my quote! It does make things so much easier on the rare occasion there is a dispute about what work is actually to be carried out.

Now I realise that we should be giving out certificates anyway as part of the work, but in your case you were told you didn't need to. This doesn't sound unreasonable for such a small job, and the NICEIC say much the same (ref Professional Electrician & Installer, 25th November 2019, Appropriate use of minor works certificate) - see below. However, it does look like some form of documentation would still be required.

I just carry out work in domestic premises. If I was having a lazy day and did not give a MWC for a fan change, I would still have made a few quick notes of the tests in my diary (Zs, RCD, circuit details). If you are carrying out hundreds of these jobs for a council I think you need to be pretty hot with the paperwork.

"Replacement of an accessory

Although a minor works certificate may be used to certify the replacement of an accessory, for example, a wall switch or a socket-outlet on a ‘like-for-like’ basis, such work would generally fall under a maintenance regime and so the client, such as a local authority, can choose to use their own documentation instead.

However, where this is the case, the safety declaration, installation details, and the inspection and test results recorded on the client’s documentation should be no less comprehensive than would be included on the MEIWC. A copy should also be retained by the contractor."
 
Last edited:
Maybe you could ask them for existing records that are up to date for each of the properties as being also a requirement for regulation compliance. Perhaps where they do not have them up to date you might offer EICR for those properties and get a scoop? Really speaking they are quite right to ask for the MEIWC. 132.15 and 514.9.1 require ascertaining the suitability of the installation. If they produce the certificates this maybe would comply as you have ascertained the current suitability?
 
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a minor works certificate.

Came into the office today to find they now want minor works certificates for about 250 fans we replaced.

Now normally if you was just doing a like for like swap no one would start checking the water/oil bonding, and recording circuit details or even looking to see what system of earth the property has, therefore my question is “since these items havnt been inspected would i be complying by simply marking most of the certificate as N/A?”

There’s simply no way we’re going to re visit 250 propertys some up to 45 miles away just to tick a box on a form that technically doesn't even need issuing for a double insulated fan swap over. i don’t want to get into a debate if it’s ethically right or wrong i just want to make sure im complying.

How iv always interpreted it was you may “n/a” something not inspected and my reasoning for not inspecting bonding would be because a replacement doesn’t require you to, therefore it must be okay to record bonding on a minor works as n/a. Do people agree?
If this is a genuine change then throw it back at them, a nicely worded email explaining the additional testing requirements and paperwork charge of £--- per unit might focus their minds a little.
 

Reply to Can you ‘N/A’ most of a Minor Works for a like for like replacement? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
919
Hi, I would like to do some minor domestic electrical work while I am completing my NVQ level 2 in electrical installations. I have the 18th...
Replies
11
Views
5K
Evening all, I just wanted to see if electrical improvers/adult trainees with appropriate levels of experience and who hold testing...
Replies
0
Views
1K
I'm sorry if this isn't in the right place but this is my first time using this forum. I'm also sorry if i make some mistakes but I'm new to this...
Replies
6
Views
1K
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
644

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock