This may be a daft question, but I have been asked to install an outside socket on a static caravan.
As is the norm on a holiday park, the supply is via a 16A 30mA RCBO installed with a meter in a weatherproof enclosure and feeds the van via 2.5mm flex on a 16A 3 pin plug.
Usually the norm would be to either spur off an existing socket, or take the feed back (if possible) to the consumer unit, however, the easiest would be to install the socket on the cable between the caravan's hook-up 3 pin plug and the consumer unit in the van, as the cable passes the area where the socket is to be mounted.
My question is.....can I do this? or does the socket have to be fed (either directly or off another socket) from the caravan's consumer unit?
I can't see any issue as, either way, the new socket will be protected by a 16A 30mA RCBO.
Any suggestions?
 
My question is.....can I do this? or does the socket have to be fed (either directly or off another socket) from the caravan's consumer unit?
I can't see any issue as, either way, the new socket will be protected by a 16A 30mA RCBO.
either take it from the existing circuit or own circuit that what I would do .
 
Only cause you are an older codger than me...
stock-vector-cartoon-grandfather-with-cane-vector-illustration-with-simple-gradients-57321424.jpg

yep.
 

Reply to Caravan outside socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
866
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
740
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock