I have just rang CED and they say there's nothing on the manufacturers instructions which says you can't install them vertically, but it doesn't say you can either.I’d ring GED and ask em if you not happy ?
But the master switch is usually along the bottom... plenty of 3 phase DBs are designed to run in that configuration. As far as I know the MCBs/RCDs will operate in any orientation,
Also seen
But the master switch is usually along the bottom
and conforms to "Normally expected"
UP-On
Down Off ... ( gravity assisted )
I'm with @Lucien Nunes " fire crew " comment.
It has been made less safe.
you point it out where it says that , maybe torque setting and nowt else .If not installed to manufacturers instruction then its a fail
Well if it doesn't say fit it how you like....but the op said it didnt comply with manufacturers instructions......maybe you should read the post properlyyou point it out where it says that , maybe torque setting and nowt else .
it makes no difference either on its side or the correct way ,the current will flowDo manufacturers instructions definitely prohibit this? Only issue that springs to mind is different heat distribution and cooling
Blimey, buzz...I thought you'd done an English Language course.....'till I got to that last paragraph.Using unapproved parts will invalidate manufacturer guarantees and may result in an unsafe installation.
so where do it says you can not turn the C/U on its side and what about three phase boards .
Mmm...another with it's kex half way down.surprised nobody's mentioned how neatly the tails are dressed.
only if you tilt your head the right way.If you tilt your head just enough then it looks the right way up....
One of the new regulations, 536.4.203, states that devices and components that are used in low voltage assemblies (to BS EN 61439) such as consumer units, and distribution boards must only be those that have been declared suitable for that purpose by the manufacturer of the assembly. Or put another way: only use manufacturer approved parts, don’t mix brands of devices or control items.
Each manufacturer of electrical switchgear designs and tests its own products for use in combination with each other, not with other brands. So if someone were to use a mixture of brands they would be creating an untested assembly and untested assemblies aren’t backed by manufacturer guarantees.
Obviously, no manufacturer can guarantee an installation that hasn’t been completed in line with the manufacturer's installation instructions. But that doesn’t mean that manufacturers won’t permit control items to be added to an assembly. Electrium, for example, offers a custom build facility and will design & build factory built assemblies that will carry a manufacturer guarantee, even if the assembly includes non Electrium products.
Readers should be aware that the notes relative to 536.4.203 state that if the assembly deviates from the original manufacturers' instructions then the person introducing that deviation becomes the manufacturer. So if you have an installation that requires non-standard arrangements talk to the manufacturer about how to provide this in a compliant manner.
Using unapproved parts will invalidate manufacturer guarantees and may result in an unsafe installation.
so where do it says you can not turn the C/U on its side and what about three phase boards .
It doesn't say in the regs....but if the manufacturers instructions say you cant then you cant.......follow manufacturers instructions......easyOne of the new regulations, 536.4.203, states that devices and components that are used in low voltage assemblies (to BS EN 61439) such as consumer units, and distribution boards must only be those that have been declared suitable for that purpose by the manufacturer of the assembly. Or put another way: only use manufacturer approved parts, don’t mix brands of devices or control items.
Each manufacturer of electrical switchgear designs and tests its own products for use in combination with each other, not with other brands. So if someone were to use a mixture of brands they would be creating an untested assembly and untested assemblies aren’t backed by manufacturer guarantees.
Obviously, no manufacturer can guarantee an installation that hasn’t been completed in line with the manufacturer's installation instructions. But that doesn’t mean that manufacturers won’t permit control items to be added to an assembly. Electrium, for example, offers a custom build facility and will design & build factory built assemblies that will carry a manufacturer guarantee, even if the assembly includes non Electrium products.
Readers should be aware that the notes relative to 536.4.203 state that if the assembly deviates from the original manufacturers' instructions then the person introducing that deviation becomes the manufacturer. So if you have an installation that requires non-standard arrangements talk to the manufacturer about how to provide this in a compliant manner.
Using unapproved parts will invalidate manufacturer guarantees and may result in an unsafe installation.
so where do it says you can not turn the C/U on its side and what about three phase boards .
I'm also doing a Chinese course has well ,how to order a meal , number 39 please you good man , wo you wan .lol.Blimey, buzz...I thought you'd done an English Language course
Since its speed is of no calibrated consequence --off gravity assisted comment,
One of the new regulations, 536.4.203, states that devices and components that are used in low voltage assemblies (to BS EN 61439) such as consumer units, and distribution boards must only be those that have been declared suitable for that purpose by the manufacturer of the assembly. Or put another way: only use manufacturer approved parts, don’t mix brands of devices or control items.
As manufacturers guidelines cannot cover 100% of circumstances then sometimes it's down to your call, you have to make the decission as to weather it's safe.
Mounting a DB sideways is NOT dangerous.
Reply to Consumer unit installed on it's side. in the UK Electrical Forum area at ElectriciansForums.net