Consumer unit replacement

Discuss Consumer unit replacement in the UK Electrical Forum area at ElectriciansForums.net

If they look like this and are hanging off the wall then maybe...just maybe!
IMG_3416.JPG
 
there is a good video thats just popped up on my youtube feed, from that bloke john ward. it covers EICR's and will give you lots of ideas, havent watched it all (its an hour long) but given a lot of his videos are quite informative might be worth a watch and help you understand various points
 
Can anyone give me a list of things from an EICR that might mean that your consumer unit might need replacing
? is this a serious question? if so please come back and explain why you asked this and maybe we can try to assist you, that said, I am concerned you are in one of two camps. 1, you want to justify replacing a DB, or 2, you have been told yours needs replacing and you are not sure.
 
Can anyone give me a list of things from an EICR that might mean that your consumer unit might need replacing
I tend to agree with the above posts, however I think I remember that you are early on in your career, so may be attempting to learn, the assessment for a CU change is more than an EICR result and to not realise this indicates a lack of awareness.
However I did go through the EICR observations for distribution boards and came up with the following, if the observation was coded for danger would the consumer unit need changing?
Consumer Unit(s) / Distribution boards
Equipment Working space / accessibility adequacy(132.1.2,513.1)- No, but perhaps moving
Security of fixing (134.1.1) – No, repair
IP rating of enclosure suitability (416.2) – possibly, possibly repair
Fire rating of enclosure suitability (526.5) ) – possibly
Enclosure not unsafely damaged (621.2(iii)) ) – possibly, possibly repair
Main linked switch present (537.14) ) – No
Main switch operation (612.13.2) ) – No, repair
Disconnection of circuit breakers / RCDs proved (612.13.2) ) – No, unless replacement PDs no longer available
Protective devices correctly labelled & identified (514.8,514.9.1) ) – No, repair
RCD quarterly test notice present locally (514.12.2) ) – No
Mixed cable colour warning notice present locally (514.14) – No
Alternative supply warning notice present locally (514.15) – No
Other required labeling present (specify) (S.514) – No
Protective Devices & bases of correct type & rating, no signs of thermal damage or arcing (421.1.3) – possibly
Single pole protective devices in line conductor only (132.14.1,530.3.2) – No, repair
Cable entries protected against mechanical damage (522.8.1,522.8.11) – No, repair
Cable entries protected against Electromagnetic effects (521.5.1) – No, repair
RCD/RCBO(s) provided for fault protection (411.4.9,411.5.2,531.2) No, unless PDs no longer available
RCD/RCBO(s) provided for additional protection (411.3.3,415.1) No, unless PDs no longer available
SPD device(s) functional (if present) – No
Confirmation that all connections correct and firm to terminals / busbars– No, repair
 

Reply to Consumer unit replacement in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock