A

amberleaf

O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Apprentices& 2392-10 )- Please take the Time to Read
:24:

This Test is Conducted on Domestic Installations .

I do this Test First . Why ??To make sure that I have a Earth returning back to Transformer Windings . External
BeforeI connect up My Earthing to the Consumer Unit.

TestSequence & Descriptions .

Thefollowing Test(s) are carried out with the SupplySwitchedOFF
ExternalEarth Fault Loop Impedance . ( Ze )

TheReason behind this Method )- To establish that a good Earth Exists at the Installation in Order for theremaining Test(s) to go ahead.
ProspectiveFault Current . ( PFC )

612.11.)- Protective EarthFault Current shall be Measured .
Bydoing this Test you have to Remove (Disconnect the Main Protective Bonding Conductor ) Earth – from the ( MET ) in the Consumer Unit . ( METMainEarthing Terminal)

TheReason behind this Method )- You are Removing Parallel Earth Paths . ◄◄◄◄
ByTesting the Line & Earth. You have a straight path to back to the Transformer Windings .

(Ze ) Measured at the Supply Position .

Onelead on ( The Disconnect the Main Protective BondingConductor ) Earth
&the Other Lead on ( At the Top of Main Switch ) Line

Younow have a Closed Circuit . ( Protective Earth Fault Current shall be Measured )

Itis one off the Easiest of all Test(s)


Line & Earth cable Only which has been Removed from ( MET ) Simple -&-s will pick your Brains on this ◄ 2392-10

-&-s)- The following Test(s) are carried out with the SupplySwitchedOFF

Apprentices( What is Ze I hear you Say ??? )
Symbolsused in the Regulation . p/36 .
Thatpart of the Earth Fault Loop Impedance whichis External to the Installation ( Ωs )
 
Apprentices: Basics
Rememberthat the : 17[SUP]th[/SUP] Edition – is British Standard :iagree:

Meaning)- ( R1 +R2 ) …. Line / R1

Meaning)- ( R1 + R2) …. CPC / R2

Putthe two together . You have ( Line / CPC ) ↔ ( Line - R1 + CPC - R2 )

Inany Exam . The Regulations will get you out of Trouble .

Toconfirm This .

Symbolsused in the Regulations p/36
( R1 ) – Résistance of the Line Conductorof a Distribution or Final Circuit (Unit )
TheRegulations are pointing you to . Appx 4 – Schedule of Test Results .

Symbolsused in the Regulations p/36
( R2 ) – Résistance of the CircuitProtective Conductor( CPC )of a Distribution or Final Circuit ( Unit )
TheRegulations are pointing you to . Appx 4 – Schedule of Test Results .

(Ze ) External to the Installation p/36
Meaning )- Outside of theBuilding → Ze ] ↔ [ Zs Inside of Building.

(Ze ) You are checking that you have agood Earth from the Transformers Winding
(Zs ) You are checking That your Installationis Earthed (Zs ) 612.9 – The Earth Fault Loop Impedance . is required to be determined forthe furthest point of each circuit

-&-s You will be asked the Qs ) Formula Calculating Earth Loop Impedance . itwill be the Option of 4 Qs ) mixed up .
( Zs = Ze + R1 + R2) ◄◄ This Qs is the start of Testing Calculation(s) for 2392-10

The colour has been added for Clarity
 
ApprenticesBasics
LearningCurve

Regulation(s)p/333

( EIC ) Electrical Installation Certificate

Weare looking under ( Main Protective Conductors )

EarthingConductor : - Material( Copper ) C.S.A ( 10mm[SUP]2[/SUP] ) … Connection Verified Tick inbox
MainProtective Bonding Conductors : - Material (Copper ) C.S.A ( 16mm[SUP]2[/SUP] ) … Connection Verified Tick inbox

Youare Confirming )- To incoming Water & / or Gas service … ConnectionVerified Tick inbox

TheEarthing is very Important in any Installation/ or Jobs

Pointto Note : Please mark your Earthing in ConsumerUnit ?? Gas / Water ( White InsulatingTape . Why ?? if you have to come backfor any Reason you can Indentify for Testing reason . Testing comes under Common Sense . Yeah

Remember that the Certificationis you Proof in a court of Law i) Your complied with British Standards . ii)As a Competent Person . Tester .
:35:
 
Testing. Yes this will come up on 2392-10 -&-s Q/As

Initial VerificationNew Installation ( Certificate )
Regulation632.4.
All)- defects or omissions revealed during Inspection & Testing of theInstallation work covered by the ( Certificate ) shallbe made good before the Certificate is issued

PlainEnglish : The regulation(s) are telling you to Cover you But .
Electricians’are not Perfect 99.9% . mistakes can bemade accidently . The Reason for Testingin Order from the Regulation(s) is that every test has a reason(s) ??

TheRegulation(s) prescribed Tests . Etc

612.2.1.Continuity of ProtectiveConductors ( Dead Test) Do we have Earthing ?? ETC .
612.2.2.Continuity of Ring Final Circuit Conductor( Dead Test ) is the Ring a Complete Loop?? ETC . Do we have reverse Polarity
612.3.2.Insulation Résistance ( Dead Test ) has the cable been damaged ?? L/N – E . Megger 1552 two leads .

500V≥ 1.0MΩ ( Mains ) 2 x 230V = 460 / 500V ( your fire up doublethe Voltage ) Testing the Cable only
SELV: = 50V .A.C. = 250V D.C. ≥ 0.5MΩ
(They are only three Qs on this matter ( Table 61 – p/158 – ( 250V ≥ 0.5MΩ ) ( 500V ≥ 1.0MΩ ) ( above 500V – 1000 ≥ 1.0MΩ )
Look at the Wording . SELV / (250V ≥ 0.5MΩ )

2392-10)- Testing Q/As -&-s Yes ◄
612.3.3.Where the circuit includes ELECTRONICE DEVICESwhich are LIKELY to INFLUENCEthe results or be DAMAGED.
Onlya MEASUREMENT between the LINE conductors connected together & the EARTHING ARRANGEMENT shall be MADE . ( L& E ) Only

Nowthe Regulations are TELLING us ????? ( CoverourButs )
NOTE 1 )- AdditionalPrecautions . such as ( DISCONNECTION ) may be NECESSARY to avoid damage to ELECTRONICEDEVICES

Nowwe can say Informative
 
Apprentice’sBasics .

Continuityof Protective Conductors . 612.2.1.

Method 1 )- ( R1 + R2 ) Line / CPCThis also proves Polarity
Method 2)- ( Measurement of R2 → or Bonding ) R2 / Wander Lead

Point to Note )- Test Voltages & Minimum Insulation Résistance .
Table 61 – p/158 - 500V to 1000V ( Above )

613.3.1. Insulation Résistance ( Domestic Installation - 500V between Live conductor(s)where appropriate during this measurement . Line & Neutral may be connected together . L/N –E separate
 
RingFinal Circuit ( DeadTest ) Loop Testing

Thereason behind this Test !!
RingLoop Testing ensures that any Ring Circuits wired in the Installation you havecreated are actually a ( RING CIRCUIT ) & not forming a ( Radial )
Figure of Eight loop

Testing must include the relevantTests from the following Checklist ( 612. )

O.S.G.(- When a Test shows a failure to comply . The installation must be corrected .The test must then be Repeated . As must any earlier test could have beeninfluenced by the failure .

Itthen chases onto the Regulation(s) 612.1.
TheTests of regulation(s) 612.2. to 612.13. where relevant . Shall be carried out &the results compared with relevant Criteria .
TheRegulation are telling us in Order . each test has its Reason

Apprentices. O.S.G. p/80 – 2392-10 will use this system

Continuityof Ring Final Circuit Conductors . p/80 – A Three-step Test is required to Verify the Continuity of the Line . Neutral & Protective conductors & the correct wiring ofthe Ring Final Circuit . Etc

Step1 )- p/81 / End to End ( MeasuredSeparately ) L/N/CPC
Step2 )- p/81
Step3 )- p/82

Youwill see ?? ( Little r[SUP]1[/SUP]+ r[SUP]2[/SUP] ) don’t get confused with ( R1 + R2 )
 
2392-10: NEW
Purposeof Initial Verification .

InitialVerification . in the context of Regulation 610.1.is intended to confirm that the Installation complies with the Design & hasbeen Designed & constructed in Accordance .
610.1. ) 611.2. ) 612.1. )
 
2392-10: ( T )
Certificates

Appendix6 of BS-7671 contains Three model forms for the Initial Certification of a ( NEW ) Installation or for an Alteration or Addition toan existing installation as follows.

Ambringing you to the Point )- Single Signature ( ElectricalInstallation Certificate)- That is you 2392-10
WhereDesign . Construction . Inspection & Testing are the RESPONSIBLY of ONE PERSON )- That is you 2392-10

ACertificate with a Single Signature MAY REPLACEthe MULTIPLE SIGNATURE form ◄◄◄
:iagree:
 
2392-10: This will come up -&-s
:sweatdrop:
Regulationp/339 . ( PIR)

Periodic Inspection Report .
Regulations )- row 5 . The “ Extent& Limitations “ box should fullyIndentify the elements of the Installation that are covered by the report &those that are not . This aspect having been agreed with the CLIENT & other interested parties before the Inspection & Testingis CARRIED OUT .

Tester. GN-3 p/19 .
Scope)- it is essential that the Inspector & the Person ordering the Inspectionknown the “ Extent “ of the Installation to beInspected & any Criteria regarding the “ Limit“ of the Inspection . ( BOTH should be AGREED & RECORDEDon the CERTIFICATE )

Regulation)- Schedule of Inspections P/340
Bottomof Page ??

NOTES : ( LIM ) ◄◄ -&-s/ Big time . PS trip up Q .
ToIndicate that . exceptionally . a “ LIMITATION“ agreed with the person ordering the work preventedthe Inspection being carried out ( Applicable for a PeriodicInspection Only )
 
2392-10: ( ADS )
:iagree:
TestingRCDs
Wherean RCD has a rated value of ( I∆n ) not exceeding ( 30mA ) & is used toprovide Additional Protection to BASIC PROTECTION the operating time of the device mustnot exceed ( 40mS ) when subject to a Test Current of ( 5 x I∆n )
 
2392-10:

Example Only . -&- ( 2 Seconds time ) GN-3 . p/56
Generalpurpose RCDs to BS 4293 .
Becauseof the variability of the time delay it is not possibly to specify a maximumtest time . it is therefore imperative that the circuit protective conductordoes not rise more that 50V above Earth potential ( Zs I∆n ≤ 50V ) it issuggested that in practice a ( 2 second )maximum test time is SUFFICENT . -&-s now you know

2392-10: Get your self a copy of ( GN-3 )
FunctionalTesting .
Operationof residual current devices .
Whilethe following tests are NOT a specific requirement of BS-7671 it is recommendedthat they are carried out . GN-3 . p/56

Q)Prior to these RCD tests it is Essential for Safety Reasons , that the EARTH LOOP IMPEDANCE is tested to check the requirements’have been met . WHY ??

( Wehave a Earth ) .. Common sense . RCD must havean Earth ( 612.9↔ 612.10 )
 
2392-10: 612.6.

4 different scenarios . requirea Polarity Test .

i)- Unit used ( Ω ) All single pole devices & circuit breakers are connected inthe Line conductor Only .
ii)- Unit used ( Ω ) The line conductor must be connected to the centre terminal ofan Edison Screw Lamp holder ( with the Exception of E14& E27 lampholders to BS-EN 60238 )These are European . They have known to be usedon exams .
iii)- Unit used ( Ω ) All polarities of Socket outlets ( Ring & Radial must be Verified )
O.S.G. – p/78 ↓
iv)- Unit used ( Ω ) The Polarity of the mains supply must be correct . [ Using anapproved voltage tester ] with the supplyconnected
 
Apprentices)- Continuity of Main Protective BondingConductor . ( PIR )

Alot off you will have a Multi Function Tester ( At this point you have zero the Megger to the test leads .
(for the sake of -&-s . if you don’t have a Megger ? you do it the old fashion way “ Subtract Leads“ Leads 0.02reading 0.4 = 0.38Ω ) you may get asked this one ??

i) Isolate Main Supply . ( Lock OFF )

( R2 ) - 612.2.1.

ii)Disconnect Bonding Conductor from Main Earth Terminal ( MET )
iii)Place One lead on conductor & other on the Earth Clampconnection ( you Using Wandering Lead )

Bonding Conductor → to Water pipe ( you have A to B – continues Loop )

iv)Zero lead Résistance & set to Ω

v)Take reading ensuring Less than ( 0.05Ω )

( Remember to replace Disconnect Bonding Conductor fromMain Earth Terminal ( MET ) BACKwhen Testing is Done )

UsefulJunk .
UnderFault conditions the Fault current should flow in a controlled manner through aCPC.

Oneother way of looking at this . A “Dedicated “ CPC would carry most of the fault current as it provides the mostdirect path & lowest Impedance back to the source of energy .
 
InitialVerification : Apprentices’

610.1. Wording .

EveryInstallation shall . DURING ERECTION ◄◄◄ ( And )on Completion BEFORE BEING PUT INTO SERVICE ◄◄◄ .be Inspected & Tested to VERIFY .Etc

PlainEnglish : Test it whilst your working on the Job .
 
Apprentices’: Basics . Yeah Reg – P/35

Youmust understand the basics .
Listedbelow are 4 terms that describe vital information in the Calculation process .

Thefirst factor you need to consider is ( DESIGN CURRENT)

17[SUP]th[/SUP]Edition - ( Ib) Design current of circuit
PlainEnglish ( Ib) Term used to describe a circuits DESIGN current in AMPS (The Load )
( In ) Rated current or current setting of PROTECTIVE device AMPS
17[SUP]th[/SUP]Edition - ( Iz) Current-carrying capacity of a cable for continuous service under theparticular installation conditions concerned .
PlainEnglish ( Iz) Term used to describe a circuits value in AMPS . once all de-rating factorshave been considered .
17[SUP]th[/SUP]Edition - ( It )Tabulated current-carrying capacity of a cable .
PlainEnglish ( It) Term used to describe the Tabulated current rating of a cable in AMPS ( The CURRENT a cable can SEFELYCARRY )

(Ib ≤ In ≤ Iz ≤ It )

Thisformula states the underlying principle of the calculation of a circuits CableSize .
 
Theprotective device current rating must be ( Equal to or Next Largest Size ) so that the circuit issufficiently protected

Formula)- used for cable calculation .

(Ib ≤ In then Iz ≤ It )

TheOver current protective device must be ( Equal to or Greater ) than the designcurrent .
 
Howto Establish the value of Volt Drop ( Vd ) Red Book BS-7671:2008

Eachcable rating in the Tables of Appendix 4 of BS-7671:2008
Hasa corresponding volt drop figure in mili-volts per metre of run ( mV/A/m )

Tocalculate the cable volt-drop ??

Volt-drop= Ib x ( mV/A/m ) x L ÷ 1000

Where.

Ib)- Design current in amps .
mV/A/m)- The mili-volts per amp per metre dropped
L)- The circuit length in metres .
1000 )- Converts the mili-volts into Volts

Scenario : ◄◄
4.0mm[SUP]2[/SUP]PVC sheathed circuit feeds a ( 6kWshower ) & has a length of run of ( 16m ) Find the total Voltage Drop . ( Vd )

i)-Work out the Design Current . ( I = P/V = 6000 ÷230V = 26.08A ) ◄ Round up to 4– 26.08695652
ii)Obtain the . mV/A/m from Appendix 4
Table( 4D5 ) p/282 .
Thevolt drop figure for ( 4.0mm[SUP]2[/SUP] T&E is 11 mV/A/m )
iii)Input all the values into the Formula & work out the Volt drop to ( Twodecimal places & add the value V )

Voltdrop = 26.08 x 11 x 16 ÷ 1000 = 4.59V

Sincethe Permissible volt drop in this Instance is ( 5% of 230V ) which is ( 11.5V ) Now does the cable in Question meet volt droprequirements . ??

( 4D5 ) p/282
FlatPVC Cables .
 
Earth Loop Impedance . 2392-10

Résistance ( Measured in Ohm’s )
Isthe property of a conductor to limit the flow of current through it when avoltage is APPLIIED . The larger the conductor is the less résistance it has .
Thesmaller the conductor is the more résistance it has . .

(Thus . a voltage of one volt applied to one ohm résistance results in a currentof one ampere ) Yeah
 
2391-10 / 2392-10
Multipliersare used by the Designer & are required toallow for one of the following .

O.S.G.Table 9B )-
Usedso the Designer can give values of Résistance at the Ambient Temperatureexpected during the Test(s) ( 20°C is classed as1 )
O.S.G.Table 9C )-
Usedso the Designer can give values of Résistance at the Conductors Maximum OperatingTemperatures .
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock