Search for tools and product advice,

Discuss Continuity Between Neutral Of Ring And Lighting Circuits in the Lighting Forum area at ElectriciansForums.net

P

paul_griff

Can anyone help with this one?

After deciding to do a periodic test on my own house (five years after moving in) I have come acrossthe following problem
The neutral of the upstairs ring has continuity (less than 1 ohm)to the neutral of both the upstairs and downstairs lighting circuits also the earths of mentioned circuits have continuity between them.

I can understand continuity between earths of upstairs and downstairs lighting circuits as cpc's are joined at two gang two way switch at bottom of stairs. But as for the rest of it i'm baffled, I have done all the obvious things like disconnecting neutrals and earths at consumer unit, removing loads (allthough no lighting transformers yet) asked my fellow electricians at work but no-one has an answer!

I have started looking under floors and finding bad things like unused live cables taped up and left under the floor and a spur taken from the ring in 1.5mm, needless to say I have rectified these and am expecting to find more such problems. Due to dodgy wiring I have found so far I will not be suprised to find interconnections between circuits somewhere, got a day off tomorrow to get to the bottom of it, so any suggestions will be greatly appreciated.
 
a possibility is that somebody has fitted an outside light, tried to take it from a switch position and, finding no neutral at the switch , has pinched a neutral from the nearest point on the RFC. something along those lines, anyway.
 
Thanks for the reply Telectrix, Outside light is a possibility but i think i have traced them both, Front one was wired on spur fed from ring main in 1.5mm so is currently disconnected and rear one appears to be fed from main junction box for downstairs lighting circuit allthough i have not followed the cable in it's entirety so will look into that. Some idiot has been playing that's for sure
 
iv'e also seen an intruder alarm panel wired L from light switch and N from a RFC JB.
 
have you eliminated a fault between neutrals and cps, u say you disconecected the neutrals form the common bar but if there is a e-n fault the cpcs would nedd seperating at the same time
 
yes I have disconnected both neutrals and cpc's from their respective common bars at the consumer unit, could be a fault between neutrals and cpc's but as it is on three circuits i'm thinking its not a cable fault.
 
Latest on this one, It is not a neutral to earth fault on the cables as when the main incoming isolator is switched off continuity between neutral and cpc's dissapears as would be expected, must be due to parralel earth paths through bonding or other circuits.
 
PROBLEM SOLVED !

I have finally traced the problem to a 30A junction box buried in the wall less than two meters away from the consumer unit. All lives were kept seperate, but neutrals were all commoned together as were earths, cowboy DIY job I'd say.
Now I just need to rewire it all properly and see if I can plaster it or if I need to get a professional in!

Thanks to all for the suggestions, much appreciatedDSCN0686.jpgDSCN0688.jpg
 
I followed offending cables from consumer unit, had narrowed the fault down to between consmer unit and first fittings upstairs so it was time to start chopping!
 
Congrats! You must have an xray machine! Thank you for getting back to the forum with your success. You don't mean plaster a JB in though, no you don't, no, nope, na.
 
PROBLEM SOLVED !

I have finally traced the problem to a 30A junction box buried in the wall less than two meters away from the consumer unit. All lives were kept seperate, but neutrals were all commoned together as were earths, cowboy DIY job I'd say.
Now I just need to rewire it all properly and see if I can plaster it or if I need to get a professional in!

Thanks to all for the suggestions, much appreciatedView attachment 9178View attachment 9179

Have'nt i told you before ? You must'nt hide junction boxes in the wall
:D
 
Last edited by a moderator:
Congrats! You must have an xray machine! Thank you for getting back to the forum with your success. You don't mean plaster a JB in though, no you don't, no, nope, na.

No, no, no, I do not mean plaster a junction box in, that's what the idiot that gave me the problem did. I fitted all new cables between board and upstairs first fittings, just need to clip and cap the cables then plaster the cables, not junction box!
 
Wish you could of told whoever put it there in the first place! I would not dream of leaving it there as my trashed kitchen wall can now testify, floor to ceiling chase and all new cables!

Just think of the satisfaction you've got from tracing a pig of a fault (forgot to say: well done on that by the way). Unfortunately you'll find a lot of that sort of thing having been done & not only by the DIY brigade.
 
but it's worked perfectly for years, judging by the green only cpc sleeving!!!
 
and well done for finding the pig. that would have had many a good spark baffled.
 
Thanks for all the praise. Now all rewired with cables going straight up the wall instead of diagonally and neatly capped waiting for the plasterer to re plaster the whole wall (had to take a lot more off to sort it out)
 

Reply to Continuity Between Neutral Of Ring And Lighting Circuits in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
687
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
774
Hi There is a lighting circuit fault in a property with the downstairs lighting circuit. I have tested the voltage and there is 230v on both...
Replies
10
Views
1K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
765
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock