You got a Reg number for that, darkwood? I've been struggling to find one.The sleeving of an identified earth is not acceptable again on paper...
514.4.2 says, "Single-core cables that are coloured green-and-yellow throughout their length shall only be used as a protective conductor and shall not be overmarked at their terminations, except as permitted by Regulation 514.4.3." This is not the case here. So I would have no issue with this, provided the core was suitably identified at both ends.
Unless you're referring to regulations or guidance other than BS7671?