Search the forum,

Discuss Cu Change Main Earth HELP! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Hi
Thanks for advice. There is 6 cottages, but all have seperate western power fuses and separate meters all in one building. The appears to be no MET here. The tails and Earth travel 30m to the CU. It appears to be the same with each of the others. Although there are 6 cottages together, they are all seperate supplies and all cottages owned by different people. Therefore I am sure the MET is at the CU? I know it sounds stupid to TT a supply when it is PME but if I the main eaarth needs to be 16mm and it cant be done without digging 30m then is it not an option?


Sorry i can't envisage the set-up your describing, any chance of a photo or two of the intake building room set-up and one of the cottage supply position??

Forget any notion you may have, of degrading your earthing system, from what you have at the moment!! It not only sounds stupid, it IS stupid!! lol!!

Thought you said the supply cable to the cottage was ducted, so why would you need to excavate?? What type of conductors/cable is being used in this duct??
 
Unless there is an extremely high or extremely low PFC, what on earth is wrong with a 10mm main earth on a 60A PME?!? Pretty much agree with that...

Required tail size is 16mm, therefore main bond will be 10mm. The main earth is sized according to the bonding conductor. Ergo sum... 10mm main earth. ...other way round!!

I wouldn't entertain using any higher than 10mm for the main earth for any supply up to and including 100A regardless of its type (PFC permitting). I don't totally agree with that statement



I just think this is a strange distribution system, from what i can make of it so far!! lol!!
 
Eng on a PME system the main bond is sized according to the supply neutral. The main earth then has to be sized according to the bonding conductor (542.3.1).

PME; size the bond then the earth.
TN/TT; size the earth then the bond.

Out of interest, why don't you 'totally agree' with my last statement?
 
Eng on a PME system the main bond is sized according to the supply neutral. The main earth then has to be sized according to the bonding conductor (542.3.1).

PME; size the bond then the earth.
TN/TT; size the earth then the bond.

Out of interest, why don't you 'totally agree' with my last statement?

Going to bed now mate, (2.30am here) get back to you tomorrow sometime!!
 
it is wrong way round. the bonding conductor/s are sized according to the size of the required main earthing conductor. and while we're on it, what is the reg. no. taht says on a pme system it's got to be 16mm.
 
If the me is 10mm on a 60 amp main cut out I would leave it, if as you say all plots have their own fused cut outs, no multie ways anywere ie ryefield units?,but if that was the case you would have a met at the supply intake.without a pic its a bit hard good luck.
 
Its not the wrong way round Tel, sorry pal. See 542.3.1

don't disagree there, basically the earthing conductor must not be less than 10mm, but that's not to say it has to be >10mm.
 
Its not the wrong way round Tel, sorry pal. See 542.3.1

don't disagree there, basically the earthing conductor must not be less than 10mm, but that's not to say it has to be >10mm.

No of course not, I don't believe I said that did I?

My point was that on a PME system you size the (minimum size of) main earth by the main bonding conductor. That's all :)
 
Eng on a PME system the main bond is sized according to the supply neutral. The main earth then has to be sized according to the bonding conductor (542.3.1).

PME; size the bond then the earth.
TN/TT; size the earth then the bond.

Out of interest, why don't you 'totally agree' with my last statement?

Haven't done too much in the way of PME for a good few years now, so i'll have to have a gander at the Reg's on Monday when i get back to the office to see what the so-called official version is. I can't remember sizing the main earth conductor from the bonding conductor on a PME install though.

Personally, i'd stick with the 50% rule, even with a PME installation for the main earthing conductor, especially in these day's of plastic service pipes becoming more and more prevalent in the domestic sector. To be honest, can't think of any domestic PME heads that i've seen, converted or otherwise, that had just a 10mm main earth coming off the heads N/E connection to the MET, (...may be some very early heads had a 10mm connections). It's always been 16mm, (or larger when when the head has been a substantially bigger 3 phase supply on a commercial or small industrial installation).


I'll go along with the 10mm earthing conductor in this instance though, for a known 60A supply!! I certainly wouldn't be leaving the PME connection behind in favour of a typical UK TT system that's for sure!! lol!!
 

Reply to Cu Change Main Earth HELP! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top