CU Change - Ring Tripping RCD Low IR

Discuss CU Change - Ring Tripping RCD Low IR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

No i didnt do any testing before i started as it was an old wylex fuse box all the wires were short and twisted together.

Unfortunately this is the fatal mistake. As much as its a total pain in the back door, it really is worth testing it to make sure it's ok, at least do global IR readings.

The issue now is that you have a board you cannot get to hold.

I ripped one out for a mate last year, it was rammed behind a cupboard and it was a non starter testing it, I got there at 8am, and didn't go home until 4am the next morning.... My stupid fault!

As for the cert, no you need to correct the problem and issue an EIC and notify, this really is the only option.
 
A few of you seem to be suprised about the none rcd side comment.
Usually a 17th dual split board as 5 x 5 rcd protection and then you get a 2way busbar that offers the option fror either a mcb or rcbo.
I always budget for 2 additional rcbo's one for the boiler and one for the cooker so in the event of a fault at least they can keep warm in the winter, have a bath and cook a meal.
I am good me.
 
A few of you seem to be suprised about the none rcd side comment.
Usually a 17th dual split board as 5 x 5 rcd protection and then you get a 2way busbar that offers the option fror either a mcb or rcbo.
I always budget for 2 additional rcbo's one for the boiler and one for the cooker so in the event of a fault at least they can keep warm in the winter, have a bath and cook a meal.
I am good me.
Hi Integrity boards should be made mandatory IMHO, far far better for now and the future
 
The Jam were awesome though
 

Reply to CU Change - Ring Tripping RCD Low IR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock