Discuss Designing an Electrical Panel with Brum Solution - Busbar Capacity Query in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I need to design an electrical panel, and the main circuit breaker is rated at 250 A. We are implementing a 100% Brum solution for the panel, but Brum's earth and neutral busbars are rated up to 125 A. If I require 20 earth poles, can I use two 10-pole busbars rated at 125 A each? Or does each earth busbar need to withstand the maximum current of 250 A from the main circuit breaker?
 
You have at least 3 issues:

First is the regulation aspect and as you seem to be located in Germany not many folks here (mostly UK-based) will know them.

Second point is already mentioned above, the busbars all need to cope with the maximum fault current & let-through (I2t). This is partly the heating effect, but also as you go above 100A then in the UK the rules start to require consideration of the electrodynamic forces that can bend conductors and physically damage them (and attached components). In a well constructed system, so internal faults are VERY unlikely, you might be able to rely on the downstream breakers to limit this but if not absolutely sure then you should consider the upstream fault current.

The third point is you have to avoid overloading the busbars. If your supply breaker is above the busbar capacity then you are relying on the sum of breakers fed off there to be lower than the maximum of the busbar. The could be exceptions if you can be use all are fixed loads so the breakers are only for fault disconnection, but in many cases you cannot be sure of that so with 10 poles on the busbar you ought to be no more than 12.5A average per pole (or whatever combination keeps the sum to 125A or less)
 

Reply to Designing an Electrical Panel with Brum Solution - Busbar Capacity Query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
860
Hi, I plan to add solar to my home and have a question about how many amps I can backfeed into my AC service panel using Net Metering. I know NEC...
Replies
1
Views
828
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
596
The seller is saying they will not upgrade the electric and it is normal to have 100 amps. However the inspector is stating it may trip often and...
Replies
4
Views
820

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock