Discuss Dim lights that gets worse as I turn on more lights in the same circuit. in the UK Electrical Forum area at ElectriciansForums.net

LLoflin

DIY
Reaction score
0
Kitchen led lights have all of a sudden dimmed by about 30% no dimmer in the system. There are 2 switches for this set of lights. Regardless of which switch I use the lights are dimmed by about 30%. The lights will not come back up to 100%. All other lights in the circuit and through out the house work with no issues. When I turn on any light in the same circuit the kitchen light dims even more but the light I just turned on is fine. I’m thinking this could be a neutral issue but don’t know where to start my troubleshooting.
 
Have you changed any light fittings anywhere recently, sounds like you have ended up with two lights in series. This used to be easy to spot when it was filament bulbs as both would glow at half brightness but with LED one can remain unlit and the other seem to work fine but they are both only getting half the voltage or so.
 

Reply to Dim lights that gets worse as I turn on more lights in the same circuit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
683
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...
Replies
4
Views
413
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
198
My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
Replies
10
Views
909

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock