Discuss Do I need three phase or not? Your advice appreciated. in the UK Electrical Forum area at ElectriciansForums.net

So this setup is going to be needed more and more often as we approach 2030.
Load management over the whole system is going to be needed as well, so CT limiting and central reporting/control will, I suspect, become a requirement for any fast charger.

Basically you can have 100+ houses on a 500kVA substation as the normal usage patterns (diversity of load use) means it is not overloaded for any significant time. But the old 'normal' did not include several 7kVA chargers (or more) running for many hours simultaneously on half of the properties!
 
Load management over the whole system is going to be needed as well, so CT limiting and central reporting/control will, I suspect, become a requirement for any fast charger.

Basically you can have 100+ houses on a 500kVA substation as the normal usage patterns (diversity of load use) means it is not overloaded for any significant time. But the old 'normal' did not include several 7kVA chargers (or more) running for many hours simultaneously on half of the properties!
If those houses have solar, then maybe it won't be so bad, and my plan is to be as 'off grid' as possible with mine, but that doesn't mean that I won't want to charge everything up at some point.
 
I'm asking you guys as I have no clue what the procedures are for upgrading to 3-phase and I'm an optimist. Don't beat me up for that :)
3-phase is good for many reasons, just not cheap!

As mentioned above, the assumption for getting 3P in the UK is high load, so you might find it becomes limited due to the local substation's capacity.

I think some EU countries traditionally had 3P to homes but at much lower currents (e.g. 30A per phase) so similar total power to our 100A but more efficient cable use (but more expensive DB/meter/etc). @Lucien Nunes has much more knowledge of that aspect!
 
If those houses have solar, then maybe it won't be so bad,
Not much use for over-night charging!
and my plan is to be as 'off grid' as possible with mine, but that doesn't mean that I won't want to charge everything up at some point.
It is a good goal, though if you really want to be able to operate in "island mode" (i.e. without grid power at all, even if just during storm damage) there are other concerns.

Mainly you need your own means of earthing (as the DNO's earth cannot be assumed if outage due cables damaged) and also your installation then needs to be able to disconnect on your own earth, which typically means RCD protection on every circuit, as few earth rods are low enough in impedance to allow over-current disconnection like the DNO supply earth normally enables.

Also it means your inverter has to be designed to operate without grid power (not the norm in solar as I think most shut down if grid is lost), and you must have a suitable relay to prevent any power being back-fed in to the faulted grid and possibly killing a DNO worker trying to repair things (a reason for them normally shutting down, along with what might happen when power is restored and maybe not in-phase with the inverter output).
 
One last thing - if you get anything done by the DNO, unlooping or 3-phase - get an isolator switch fitted at the same time.

Not only will it make any future work on your system easier and quicker, but should you get a PV/battery system that is capable of island mode operations you can test it by switching off the DNO supply for a couple of hours to see that it works, and keeps working on restoring the power...

Test both night and day times, just to be sure PV charging work in island mode and that it still behaves on battery alone, etc.
 

Reply to Do I need three phase or not? Your advice appreciated. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
732
Good Afternoon All I have quoted for the installation of an EV Charger that is located in an underground car park. I don't install many however...
Replies
2
Views
1K
I have a single 7kW EV charger that serves three holiday cottage. The supply to it is E7, with the night rate currently at exactly half the day...
Replies
7
Views
3K
  • Article
Electrical2Go - Green2go Launches for All Your Solar, EV Charging and Renewable Needs Green2Go - for All Your Solar, EV Charging and Renewable...
Replies
1
Views
300

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock