Hi all - been an idiot / schoolboy error - drilled into a wire that drops down to a fused spur socket in the kitchen (for washing machine I think) - blew 30A fuse for downstairs sockets and tripped RCD. The wire is behind plasterboard.
Any advice on what the repair should be would be appreciated before I call someone in.
Any idea what this should cost?
 
  • My first reaction is always make the joint meet or exceed the OCPD, so 32A is bound to be OK.
  • Another way of looking at it, is to make sure the joint is not the weakest link. If you look at 2.5mm T&E CCC (such as Table 7.1(iii) in the OSG) then it is not more than 27A, so that would be another option.
  • However, the real question is what is needed for RFC leg rating? As @Pretty Mouth has already listed it is explicit in regulation 433.1.204 but you could deduce that from looking at the acceptable methods for a 2.5mm RFC, which are (from OSG Table 7.1(i) on page 75) methods 100, 102, A & C, and of those the lowest rating is method 'A' at 20A.
 

Reply to Drilled into wire in kitchen in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top