Currently reading:
earth cable supplying tt earth spike

Discuss earth cable supplying tt earth spike in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

U

ukpablo

I have looked at table 4.2 on page 29 OSG regarding cable conductor sizes supplying earth rod, but what size generally do u use for this purpose?

i.e do u just run a 16mm everytime??:confused:
 
The minimum main earth conductor size for a TT system is 10mm. 16mm is over spec so therefore more than acceptable.
 
The minimum main earth conductor size for a TT system is 10mm. 16mm is over spec so therefore more than acceptable.


The Chinese are buying up all the copper,so we need to go easy on its use :)
10mm indeed :eek:


Bearing in mind the system needs only carry 30m/amp to operate the rcd,the size of cable to carry that current can be much ,much, smaller than 10mm

10mm is good to work with though,so thats my choice :)
 
thought 6mm, mechanically protected was ok, or am i talking krapp
 
was checking the size of tt cable requirement the other day and it is 2.5mm if not subject to corrosion or mech damage other wise 10mm min if sleved copper. if memory serves me right. I used 10mm since relatively easy to work with and what I have in van.
 
Have just checked and I stand corrected. 2.5mm protected against corrosion and mechanical damage otherwise 4mm however I always use 10mm. However as the main protective bonding conductors must not be less than 6mm I wouldn't use a smaller main earth conductor.
 

Reply to earth cable supplying tt earth spike in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top