I think their preparing the ground for combined AFDDs and RCBOs where there is a need to switch off the neutral, also 536.3.1 mentions RCDs needing to be switched for all live conductors.
 
Wonder why that is ?.
There is no requirement to switch/disconnect the neutral during over current conditions for a TT or TN arrangement except for certain requirements in part 7
I know, maybe you should ask Schneider.
 
I think their preparing the ground for combined AFDDs and RCBOs where there is a need to switch off the neutral, also 536.3.1 mentions RCDs needing to be switched for all live conductors.
No such regulation exists in bs7671 536.3.1 I mean
 
Last edited:
I miss typed it should be 531.3.1got over excited being on the forum!
That’s for IT earthing arrangements.

Except where 531.3.1.201 applies.
531.3.1.201
For protection against electric shock there is no requirement to disconnect/switch the neutral in TT or TN systems
It would mean that all single pole rcbos are non compliant even on TN arrangements.

Also 531.2.2.201
 
Last edited:

Reply to Earth Fault Loop Impedance... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top