Discuss Earthing Arrangement (TN-S or TN-C-S or a Frankenstein Creation?) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Evening Chaps

As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting an TN-S Earthing Arrangement, however a Main Earthing Conductor can be seen coming from the supply head to the MET suggesting a TN-C-S Earthing Arrangement. So thoughts and suggestions on what I would show this as on an EICR? MTIA Clarkie
6 TN-S or TN-C-S.jpg
 
Last edited by a moderator:
Ze came back as 0.11 ohms so within tolerance for either!
Even if its TN-S at the intake its probably TN-C-S 100 yards down the road.

Speaking with DNO engineers, repairs and replacements are TN-C-S. This is all urban, not sure the same applies in rural networks.

Vaguely remember on my, only used once, EV charger course they recommend treating everything as TN-C-S for the above reason.

A quick resistance measurement N-E will only confirm its definitely TN-S. Depends if the earth is passing through the cut-out or is linked to Neutral inside.
 
I would say it is best to take every supply as TNCS as you don’t know what they have done repairing and altering the supply cable down the line. I have seen aluminium concentric joined to old lead paper making the supply TNCS
 
Ze came back as 0.11 ohms so within tolerance for either!
Was hoping you might come back with 2 Ze results one to the sheath (TN-S) and one to N (TN-C-S) for PME. but if both the same it must be PME but as per post#4 speak to DNo to be sure.
 

Reply to Earthing Arrangement (TN-S or TN-C-S or a Frankenstein Creation?) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've tried to understand one way or another but this seems to be connected to the DNO fuse/cutout, and then loops down (out of sight) and comes...
Replies
2
Views
742
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
736
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
442
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock