There could be multiple faults here, a fault which has resulted in a voltage appearing on the cases of equipment, and another fault which has led to the cases of the equipment not being connected to earth.
The last time I had a similar fault was after someone had fitted their own metal light switches, surprisingly had connected the CPC to the metal switch plate correctly. When I got there they were claiming to feel tingling when touching some of the light switches.
I found that when screwing back the metal plates they had nicked one of the live conductors shorting it to the CPC. But the CPC was not connected to earth so the effect was to make all of the metal switches live with reference to earth. Thanks to the wooden floors in the house nobody got a severe shock from this.
With Further investigation I found a joint box under the floor which had all of the CPCs stripped and sticking out waiting to be connected, I can only assume the person who rewired the house put the lid on the JB and forgot to then connect the CPCs (it was done in the era of connecting CPCs outside the JB)
The last time I had a similar fault was after someone had fitted their own metal light switches, surprisingly had connected the CPC to the metal switch plate correctly. When I got there they were claiming to feel tingling when touching some of the light switches.
I found that when screwing back the metal plates they had nicked one of the live conductors shorting it to the CPC. But the CPC was not connected to earth so the effect was to make all of the metal switches live with reference to earth. Thanks to the wooden floors in the house nobody got a severe shock from this.
With Further investigation I found a joint box under the floor which had all of the CPCs stripped and sticking out waiting to be connected, I can only assume the person who rewired the house put the lid on the JB and forgot to then connect the CPCs (it was done in the era of connecting CPCs outside the JB)