Discuss EICR and 4mm2 DNO TNS EC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

NickD

Anyone care to comment on my reasoning, calculation and conclusion here?


I'm doing an EICR on a TNS system, with copper 4mm2 DNO earthing conductor (insulated) between main supply cable and MET (and then 16mm2 earthing conductor to CU and 10mm2 MPBCs). DNO fuse is BS1361 Type 2, rating uncertain because being certain would involve pulling the DNO fuse (see separate thread).


No mechanical protection present, therefore Space Corps Directive 543.1.1 mandates a base level minimum CSA of 4mm2, which is satisfied.


Calculating minimum CSA by adiabatic as per Space Corps Directive 543.1.1 and 543.1.3, PFC measured at the tails into the CU main switch is 1.78kA. To get worst-case disconnection time of the DNO fuse at this fault current, assume highest possible fuse rating, i.e. 100A; the table accompanying the BS1361 curves (annoyingly not given in the standard, whywhywhywhywhy) gives disconnect time of 0.1s (that's actually for 1.8kA fault current, but near enough). k from Table 54.2 assuming insulation is thermoplastic is 143. Hence minimum CSA is (√(1780x1780x0.1))/143 = 3.94mm2.


So I conclude 4mm2 conductor meets the stated requirements of the relevant Space Corps Directives and requires neither code nor comment on the EICR.


However I am conscious that an addition of as little as a hundredth of an ohm or so to the fault loop would increase the fuse disconnection time to the point where the installation no longer complies. I note what the details of the adiabatic calculation says ("fault current for a fault of negligible impedance"), but I worry that if one measured/considered the PFC further 'into' the CU but still upstream of the MCBs, between a bus bar and neutral bar say, then one would get that slightly smaller PFC, longer DNO fuse disconnection time and a non-compliant result. (I'm probably overthinking here but that's all my brain knows how to do really.)
 
If you feel there is a problem with the dno main incomming earth you give them a call, otherwise it's not your concern. In this situation they would laugh it off and consider it a wasted visit, as long as it hasn't been interfered with.
Ze measurement???.... about 0.13 ? seems OK.
 
Last edited:
Ze measurement???.... about 0.13 ? seems OK.

Yes, sorry. Ze measured at tails 0.13. (Confession time, just realised I took the EC out of the CU earth bar to measure Ze without parallel paths but left the MPBCs in place at the external MET. Pillock.)
 

Reply to EICR and 4mm2 DNO TNS EC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
801
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock