Discuss EICR in HMO in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
9
Carried out an EIRC at an HMO. This only concerns issues found on the CU.

  • Neutral bar loose and snapped from casing.
  • Neutral linkon both RCDs damaged.
  • One breaker incorrect branding.
  • jagged saw marks cut out of CU casing (plastic).
  • One RCD only just passed its times trip test.

My issue is I have recommended a new CU. As it’s a small board and I can source the new CU for £60 (yes customer has a tight budget).
I have to change the tails anyway as they are two small and add two new socket radials. As sated the CU is only small so wouldn’t take long to swap anyway. The customer has said they can get second hand parts for this CU off another CU in another HMO. The CU is no longer manufactured and I don’t feel comfortable installing second hand parts into the CU. What would you do?
 
Nope not for me sounds like you’d be saving up grief for ya self, get paid give them the report quote for works job done.....that’s a small unit for an HMO mate, How many circuits are there and how ya gonna fit spd AFFD etc if needed?
 
Lets face it you can get a 6 circuit populated CU from screwfix for £60 and save yourself the dilemma of 2nd hand parts:
https://www.NoLinkingToThis/p/briti...d-high-integrity-dual-rcd-consumer-unit/4674g
 
You should have no concern for their budget. Quote for a new unit with spd it is up to them what they do, forget any used parts you can only guarantee what you provide.
 
Yeah tiny board mate. 1 lighting circuits one socket circuit, shower and cooker. Circuits actually test out ok with a few C3’s. Iv recommended a rewire to separate circuits etc. No SPDs or AFFDs and the owner have signed a document saying they don’t want them after Iv explained the reasons. HMO licensing any NIC are happy Iv recommended and they have declined
 
HMO’s do seem to be the lucrative rental market these days. I see they’re usefulness in housing single people, but the rent per room is way more added up than say one family renting the entire house. And that’s taking the landlords extra expenses into consideration.
Not many around here. Too many ex council one bed flats and non registered private lets
 

Reply to EICR in HMO in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Recently been working on a system design for a LL. I was told the building would be a three floor 16 room HMO, so the design was done to the...
Replies
34
Views
5K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
273
Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
810

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock