Discuss ELCB,s.How do they work? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
126
I know they are a bit old now but they are still used a lot in countries like Thailand.

As far as I understand it an ELCB would be used on a TT system or where there is a high impedance earth loop.
A remote rod is put down into the ground say outside the property and this is then connected to the properties MET/ earthing/CPC system.

During an earth fault the fault current will try to make its way through the property CPC and then to the rod, the fault current will then try to find its way
through the ground and back to the star point of the transformer.

Because the resistance of the rod is quite large a voltage or volt drop will develop between the metalwork in the house and the rod and when this voltage
rises above say 50 Volts the ELCB will switch off the supply.

Inside the ELCB is a sensing coil that measures the difference in voltage between the metalwork inside the house and the ground rod outside.

Is this correct, is this the best way of looking at it?

Any comments appreciated.

Thanks.
 
I'm guessing inside the ELCB is a coil, a coil that has a certain resistance and when a current flows through that coil a volt drop will appear across it, the more current that flows through the coil the higher the volt drop will be between both ends of the coil.

When the volt drop between both ends of the coil becomes 50 Volts or greater the ELCB will switch off the supply.

Is that correct?
 

Reply to ELCB,s.How do they work? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582
Short version: does code specify a minimum distance from the panel to the first grounding rod, and if so, what is that distance? Long version...
Replies
1
Views
588
If we had 4 appliances to power, one in every room of a house, Once the current passes through them all, the remaining voltage & current is said...
Replies
12
Views
2K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock