Hi Guys

After some advice please ;-)

Doing bathroom at home putting electric UFH heating in, only every used same make together: warmup mat and warmup programmer.

Question is I have 2 x Heatmiser Neo stats currently doing rads & UFH(wet) elsewhere in house.
So want to stick with Neostat.....

- Would there be any issue me using a different make from warmup on their UFH mat ?

heatmiser-neostat-e-v2-glacier-white-electric-floor-heating-thermostat

..... cant see why not ?

Thanks Sy
 
depends .if you are using the stats as room temp sensors, should be OK, but the ufh stats have in floor sensors to measure in the floor itself.
 
Yep it will work fine. You can adjust the settings in the neostat to work with any floor probe, but best if you use the probe that comes with the stat.

The manufacturer of the heating element itself is irrelevant. I normally use ‘heat mat’ and neostats
 
Yep it will work fine. You can adjust the settings in the neostat to work with any floor probe, but best if you use the probe that comes with the stat.

The manufacturer of the heating element itself is irrelevant. I normally use ‘heat mat’ and neostats
ok mate cheers.... for some reason I've always used warmup mat & stat - though it was something to with warranty.

Neo stat much better ;-)
 
The combined air and floor stats seem to be more accurate for controlling the room temperature, notwithstanding it is the most expensive form of heating, now Air Source Heat Pumps on a wet system of floor heating much less expensive and very accurate IMO.
 

Reply to Electric UFH in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning Guys Anyone else get fed up with plumbers/ builders supplying UFH (wet & electric) gear and it's the cheapest load of cr@p !! Had enough...
Replies
1
Views
1K
All of the UFH thermostats that I have ever fitted have had the air temperature sensor integrated into the hard-wired wall mounted programmer...
Replies
4
Views
1K
Hi all, I have a slightly mish-mash heating set up, in that downstairs I have wet underfloor heating with an individual thermostat per room, but...
Replies
1
Views
2K
Carried out an EICR and am now doing the remedials. Poor IR results on conservatory ring which I have now identified as the electric UFH. The...
Replies
17
Views
2K
I have a customer with a problem of RCD tripping caused by the wet UFH systems. There are 5 UFH areas each with a Wilo Para pump attached. Along...
Replies
29
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock