J

james101

Morning all,

I've just got a quick question regarding the electrical installation certificate and the supply characteristics & earthing arrangements section. I'm due to complete an installation on an industrial site and follow up with all the relevant tests. The details of the installation are as follows:

Main supply to site to Substation No1 - 3 phase
Feed from Sub No1 to Sub No2 - 3 phase
Existing single phase single way dis board in Sub No2 feeding new 12 way consumer unit
New 12 way consumer unit to feed existing 8 way consumer unit

It may be a daft question but am I right in thinking the supply characteristics section relates to the existing single phase single way dis board in Sub No2? Also, will I need to do two separate electrical installation certs for the new and for the existing consumer units? Or can I incorporate them both onto one cert?

Thanks
 
Supply characteristics is the incoming supply from the DNO.
But if that incoming is HV with HV distribution within the installation as your post suggests then it is beyond the scope of 7671.
 
Thanks for the reply.

There is HV distribution from Sub No1 to Sub No2, and from Sub No2 there is both HV and LV distribution. My installation is only concerned with the LV distribution, so where does this leave me with regards to my original post?
 
The single phase board sounds like it is the origin for this installation.
You are only replacing / installing the 12 way board so your EIC relates to that.
If you are also testing the 8 way then you do an additional schedule of test results (and possibly inspections) for that board under the same EIC.
 

Reply to Electrical Installation Certificate in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Is it acceptable to lim on eic for supply characteristics? I had a job in a hospital today and I couldnt gain access to the Switch room and the...
Replies
9
Views
1K
Hi all, Been asked to quote an EICR on a fairly large installation. Approx. 400 circuits that are a mixture of single and 3 phase. This is across...
Replies
22
Views
3K
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
3K
We had a new supply installed this week. DNO installed new cut out and fuse externally. Meter operator sent his engineer to move the meter in the...
Replies
12
Views
2K
Hi all, Looking for someone to help with this dilemma. Image attached to try and explain it better. We have 3 separate lights currently...
Replies
3
Views
664

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock