I have external lights switched through a contactor. I need to put in an override switch and they need come on via a photocell and be switched off by a time clock.

how do I wire it?

- - - Updated - - -

The override is to override the lights on by the way
 
The switch wire from the photocell will switch the coil circuit but how do I wire the timeclock into it to switch that switch wire thus dropping out the contactor?
 
Dru I don;t want to sound rude but this is basic stuff really, have a look at some basic control circuits you could pick up some pointers
 
I know it's basic, that's why it's ****ing me off. I know how to do it but I can't figure it out for some stupid reason.

there aren't any volt free contacts on the timeclock. There is a permanent live, neutral and switch live
 
I have external lights switched through a contactor. I need to put in an override switch and they need come on via a photocell and be switched off by a time clock.
how do I wire it?
The override is to override the lights on by the way
supply to timeclock then to photo cell and then onto contactor coil, a seperate switch for override reasons parralled up with the time clock straight onto the coil. if the timeclock switches on it will send power to the photo cell, if the photo cell calls for a supply because it has gone dark it will then send a supply to the coil. When the timeclock switches off it will cut the supply to the photo cell regardless of whether it is dark or not so you have what you desire, as well as that if you have a basic light switch with a feed to it and the switch wire back to the same connection on the coil as the photocell switch wire to the contactor then it will work.
 
Don't give me a hard time of the poor quality of the drawing, I have just scratched it down with a ink pen in 20 seconds flat lol, it could be neater and the line drawing much better, but it should give you an idea
 

Attachments

  • img006.jpg
    94.7 KB · Views: 86
Wiring like that MDJ, dependent on what type of time clock you use would limit as to when the lights could be switched on by the photocell.

Unless that's what the O/P wants and I've misread
 
Wiring like that MDJ, dependent on what type of time clock you use would limit as to when the lights could be switched on by the photocell.

Unless that's what the O/P wants and I've misread
I thought he meant the timeclock had to control the photocell, if not fine I can redraw.
 
Thanks for the help. It's so blindingly obvious when someone else lays it out like that. I was trying to go to the photocell first and hadn't looked past that. Feel stupid now. Thanks for the assistance
 
Thanks for the help. It's so blindingly obvious when someone else lays it out like that. I was trying to go to the photocell first and hadn't looked past that. Feel stupid now. Thanks for the assistance
No worries, is that what you meant? Rob thinks you meant something else?
 
Last edited by a moderator:
Just dependent on the model used. A sangamo would operate fine as you've drawn it.
I was just chucking some info down on a drawing to help RoB, if he wanted a professional drawing done I am very capable, but 20 seconds with a bic is the best I can give right now fella.
 
I would have it with the photocell output feeding the n/o volt free contacts on the timer to then feed the coil of the contactor, done that way it avoids the lights turning on momentarily every time the photcell is powered up by the timer during daylight hours. (Especially in the summer months)
 
I would have it with the photocell output feeding the n/o volt free contacts on the timer to then feed the coil of the contactor, done that way it avoids the lights turning on momentarily every time the photcell is powered up by the timer during daylight hours. (Especially in the summer months)
Would you post a picture up of that stan?
 
I would have it with the photocell output feeding the n/o volt free contacts on the timer to then feed the coil of the contactor, done that way it avoids the lights turning on momentarily every time the photcell is powered up by the timer during daylight hours. (Especially in the summer months)

Agreed.
Needs a 4 wire clock to do it right though (volt free contacts).

Boydy
 
What is the purpose of the contactor in your drawing Stan?
you have combined the control circuit with the lighting circuit, therefor why the contactor?

Boydy
 
What is the purpose of the contactor in your drawing Stan?
you have combined the control circuit with the lighting circuit, therefor why the contactor?

Boydy

The OP wants to use the timer and photocell to switch a contactor, but if it's only switching a few amps it aint needed. Also if configured slightly different the contactor could be used to switch banks of lights such as high bay and the like, but I showed it like that as I was using Mike's circuit. Don't really know why the op wants a contactor anyway.

Edit:
But you're right it's pointless unless it has it's own feed, It defetes the object really. I should've pointed that out really!
 
Last edited:
Okay,this is how I'd do it if using a contactor.<br>
<img src="http://www.electriciansforums.co.uk/attachment.php?attachmentid=23321&amp;stc=1" attachmentid="23321" alt="" id="vbattach_23321" class="previewthumb">

....And for loads >1kW IMG_2297.jpg
 

Attachments

  • IMG_2296.jpg
    89.8 KB · Views: 32
Last edited:

Reply to External lighting wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
620
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Is the following set up possible with a 3 Gang 2 Way Smart Wifi Switch set up (the black glass type touch ones) One of the 3 switches, switches...
Replies
2
Views
564
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
328
I've had a search, and found an old thread from 2016... but was wondering about modern views on this situation. I've come into possession of...
Replies
5
Views
393

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock