Discuss Faultu isolation switch readings in the UK Electrical Forum area at ElectriciansForums.net

D

Ducksy

Hey peps.

As on many occasions doing my electric shower repair rounds, I came across a faulty DP 40a pull cord shower isolation switch.

Why it is I always get a reading of about 70v between L-N load side when these switches fail.

It's always puzzled me why not 120v or 180v......nope always the 70v mark.

And the reading between N-CPC is 200v ? Why is that.

Could someone please explain the reason for this and what is actually happening inside the isolator switch for me to get readings like this.

Thanks.
 
Well first of all you will be testing with a multimeter fine but these will also pick up induced or ghost voltages that just confuses things now for me I change a lot of 40A DP pullswitches and a lot of it is due to the contacts breaking down or welding on in some cases or the main culprit is slack connections. What people do not realise is copper cable gives so when you connect them into the switch you should leave it for 5 minutes after and then check the connections again.

This also happens on cooker circuits
 

Reply to Faultu isolation switch readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Recently my RCCB keeps keeps tripping intermittently. It can happen between several hours to few days when a trip will occur. During the trips, no...
Replies
35
Views
4K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
6K
I have come across a fault that I am struggling to find. I cant remember being stumped like this before as I like fault finding and have always...
Replies
68
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock