This is the specific answer to the original question. It suggests that your MCB is single-pole (some European installations use SPSN or DP MCBs) and only disconnects the line. When the short occurs, there is a path through any other loads for a small current driven by a small difference in voltage between neutral and earth, tripping the RCD. That voltage is too low to be detected with the handheld tester.

What was confusing was your comment that 'fuses blow when...' Normally we wouldn't use that description for an RCD trip because the MCB is equivalent to a fuse, not the RCD, and any short that trips an MCB tends to create a bang!
Sorry for the confusion.
Does the RCD trip because it detects a slight current going to the ground? because it says 63 Amps on it.
 
RCDs used in the UK for additional protection trip at a level between 0.015 and 0.03A of current imbalance. Yours may be different according to the purpose for which it has been installed, although the trip current will be clearly marked on it as IΔn (I-Delta-n, the differential current). The 63A refers to the maximum load it is rated to handle and has no relationship with the tripping sensitivity
 
There's no 'culprit', the behaviour is quite normal. It might be the power factor correction capacitor in it that is providing the path from switched line to neutral.

The only thing wrong in the present equation is using that nasty pen thingy to prove dead.
If a capacitor discharges through me when i change a bulb in the bathroom I assume it could be dangerous. Is this normal? Because I really always just turn the switch off before replacing a bulb. Have I been playing with my life all that time? It says 63 Amps on the RCD.
 
Capacitors in light fittings store very little energy and are normally designed self-discharge within seconds, even if they happen to be charged at the moment you open the switch. There might not even be one, especially if it is a small light. I was merely giving an example of a possible path for the trip current based on the little information I had about your bathroom!
 
RCDs used in the UK for additional protection trip at a level between 0.015 and 0.03A of current imbalance. Yours may be different according to the purpose for which it has been installed, although the trip current will be clearly marked on it as IΔn (I-Delta-n, the differential current). The 63A refers to the maximum load it is rated to handle and has no relationship with the tripping sensitivity
Okay I see it also says 30 mA in smaller type. I get that there's no danger then. I'm going to test with my tongue.
[automerge]1586260567[/automerge]
Thank you all for the helpful replies. I guess I was just scared for nothing.
 

Reply to Fuses blow when I put phase and ground wires in contact even when light switch is turned off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
372
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
933
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Plasterer has been in this week and after leaving today, he left the light on in the room. I went to the room to turn the light off and saw the...
Replies
40
Views
4K
Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock