Currently reading:
Fusing Fans to manufacturers spec

Discuss Fusing Fans to manufacturers spec in the UK Electrical Forum area at ElectriciansForums.net

N

nickblake

Well chaps ive been looking at the manufacturer requirements for fusing down fans ,an every one appears to require only the permernant live to be fused so having words with those nice people at scolmore click you can do it easily with the grid range that doesnt actually look like grid fuse and an isolator in the same switch brilliant thats what i say good old Click scholmore GEDC0500.JPG
 
I believe only the permanent live needs fusing as the switch live just 'switches' the actual fan motor only ever runs off of the permanent live. They don't really care about the fuse blowing and leaving a permanent feed at the fan.
Saying that though, I have yet to see a fused fan in a house.
 
I believe only the permanent live needs fusing as the switch live just 'switches' the actual fan motor only ever runs off of the permanent live. They don't really care about the fuse blowing and leaving a permanent feed at the fan.
Saying that though, I have yet to see a fused fan in a house.

suprising isnt it i always put them in well since ive worked for myself
 
I believe only the permanent live needs fusing as the switch live just 'switches' the actual fan motor only ever runs off of the permanent live. They don't really care about the fuse blowing and leaving a permanent feed at the fan.
Saying that though, I have yet to see a fused fan in a house.
Come and look at some of the houses in Dorset then.
 
Looking at fig 4 on that drawing it appears to be based on a seperate switch for the fan as you have L and N coming in with a fuse in the live then it splits and a perm live goes to fan and one goes through the switch,obviously someone has very little knowledge of how fans are wired over here i.e switched with light.typical manufacturer type of thing really .
 
Sorry to re-open this one, but just wanted to confirm something. I've always believed that when the instructions state that only the perm line needs fusing at 3amps, then this means at the fan, hence the switched line is not fused. To fuse it to encompass both with one fuse would surely mean fusing the bathroom lights at 3amps as well. Seeing as the click accessory has only one fuse, I take it I am correct in assuming that perm live is referring only to the actual perm live feed to the fan? Sorry to be a bore.
 
could someone let me know which makes of timed fan only require the perm Line to be fused as all the ones i fit are the same as in post 24 that shows both perm and switched needing fusing. Would be nice to not have to put the light on the fuse as well.
 
could someone let me know which makes of timed fan only require the perm Line to be fused as all the ones i fit are the same as in post 24 that shows both perm and switched needing fusing. Would be nice to not have to put the light on the fuse as well.

Try making the fan work with just the switched live and neutral!

I assume the perm line actually feeds the motor etc. and makes the switched live useless if not present.
 
If you fit Vortice or Solar & Pallau fans the manufacturers instuctions only require a "multipole switch for isolation" so makes the whole fusing down argument redundant.

All manufacturers instructions I've seen require the fuse to be in the line BEFORE the split for the switched live.
So IMHO although the original post looks good I don't think it would hold water in a court of law IF anything went wrong, and surely thats the reason we bend over backwards to follow nonsensical regs and manufacturers instructions.
 
If you fit Vortice or Solar & Pallau fans the manufacturers instuctions only require a "multipole switch for isolation" so makes the whole fusing down argument redundant.

All manufacturers instructions I've seen require the fuse to be in the line BEFORE the split for the switched live.
So IMHO although the original post looks good I don't think it would hold water in a court of law IF anything went wrong, and surely thats the reason we bend over backwards to follow nonsensical regs and manufacturers instructions.

I've seen plenty of one-sheet poor-English instructions that state only something like 'Permanent Line must be fused down at 3amps'.
 
To be safe I think I'll start fusing the whole bathroom lighting at 3a then no-one can send me to jail for anything...
That's the easiest option. With the vast majority made in China and with **** poor installation instructions it's hard at times to work out what they want.
 
To be safe I think I'll start fusing the whole bathroom lighting at 3a then no-one can send me to jail for anything...

isn't that what we'd be doing by wiring as per fig 4 post 24? do people really wire fans this way? when the fan is isolated, so is the feed to the light? isolator and fuse after the ceiling rose, surely
 
Whilst I agree that the fuse is fairly pointless since the circuit is protected by a 6A breaker (fires notwithstanding) since most manufacturers state the fuse should be before the light this is what I would tend to do.

If you only fuse the permanent line going to the fan then if the fuse goes you can still supply a line to the fan (that may now be in a dangerous state if it has overheated or such) by switching on the light. I do not know if the SL is just an electronic run signal to employ the PL or if the two lines are commoned up in the fan, but if it is the latter then you could be trying to operate the fan once it has blown the fuse and presumably cause the fire that was averted by the fuse blowing, or trip the 6A lighting if it is a more direct fault. If the former then there can still be a line supplied to a damaged circuit board which cannot be good.

e.g. with just PL fused: switch on bathroom light, fan starts, switch off bathroom light, fan overrun continues, you leave, five minutes later fuse goes, later you come back, switch on bathroom light, fan bursts into flames or all the lights go out.

With supply fused: switch on bathroom light, fan starts, switch off bathroom light, fan overrun continues, you leave, five minutes later fuse goes, later you come back, switch on bathroom light, no light, oh dear something has gone wrong, better find out what it is.

I think the two options are as shown in this borrowed and modified diagram and I would definitely prefer my fuses to isolate the whole supply and not just one leg of it.

Good
extract fan wiring.jpg
Bad
(in my opinion)
 
All combos can be acheived by using the grid switch setup, so don't see the problems.

Fitted one yesterday and had the fan on a separate switch to the lighting, fitted along with a fuse module.

So it was a 3 gang plate with a fuse module - switch for fan - switch for lighting, then 3 pole iso in loft local to the fan.

Jobs a good un
 
Whilst I agree that the fuse is fairly pointless since the circuit is protected by a 6A breaker (fires notwithstanding) since most manufacturers state the fuse should be before the light this is what I would tend to do.

If you only fuse the permanent line going to the fan then if the fuse goes you can still supply a line to the fan (that may now be in a dangerous state if it has overheated or such) by switching on the light. I do not know if the SL is just an electronic run signal to employ the PL or if the two lines are commoned up in the fan, but if it is the latter then you could be trying to operate the fan once it has blown the fuse and presumably cause the fire that was averted by the fuse blowing, or trip the 6A lighting if it is a more direct fault. If the former then there can still be a line supplied to a damaged circuit board which cannot be good.

e.g. with just PL fused: switch on bathroom light, fan starts, switch off bathroom light, fan overrun continues, you leave, five minutes later fuse goes, later you come back, switch on bathroom light, fan bursts into flames or all the lights go out.

With supply fused: switch on bathroom light, fan starts, switch off bathroom light, fan overrun continues, you leave, five minutes later fuse goes, later you come back, switch on bathroom light, no light, oh dear something has gone wrong, better find out what it is.

I think the two options are as shown in this borrowed and modified diagram and I would definitely prefer my fuses to isolate the whole supply and not just one leg of it.

Good
View attachment 14251
Bad
(in my opinion)

with that diagram, you switch off the D/P isolator to work on/replace the fan, but you're working in the dark , as the light is fed through the isolator.
 
The way I am thinking is similar to the top diagram but with a triple pole isolator before the fan instead of the DP one at the start. OK, the lights will be off if the single fuse blows, but at least the homeowner will know something's up. But the fan can be isolated without isolating the lights as well.
 
The diagram was taken from a manufacturers leaflet and they do not require the triple pole isolator but they do require a DP isolator at "source", the TP isolator is a guide to the building regs recommendation so is not shown on the diagram. To comply with all suggestions there would also be a TP isolator on the three live conductors going into the fan.
If the customer allows me to that is how I wire extract fans: DPSFCU, Light switch, TP isolator, fan.
Amp Davids suggestion is also valid since the fuse is still before both line and permanent line, however you cannot have a timed overrun based on the light switch in that case. The only way to do that is to take the supply to the click unit from the light switch and this then means there is no local DP isolator, however the CU main switch would cover that (not what they intend but would meet the instructions and any way why does a light require a DP isolator so the 3P isolator for the fan could be considered over and above the manufacturers instructions).
 
yes mcb's are there for a reason for over load and fault protection , so no isolators for showers cookers ,

the fan timer circuit only requires the perm live to be fused as the switch live goes into the circuit componets which is basically a transistor that when the SL is operated switches the transistor on which operates the timer circuitory ,but the timer circuitory is fed via the permernant live hence only the permernant live is required to be fused as without the rest of the circuitory operating the switch live will basically only operate to the collector of the transistor and go no where else bit like sticking a termal block on a wire
 
I read earlier in this thread that the reason for the requirement to fuse a bathroom fan was because of fires that occurred with them in the past.

How effective is a 3 Amp fuse on a device that draws possibly 30watts as a fire prevention measure? The fuse is rated at around 20 times the normal operating current. Maybe I'm missing something obvious.
 
I received the ELECSA "Spark" newsletter today with an article on fusing fans. So I thought I'd drag this back up. By coincidence I was talking to my mate about lighting circuits today. We were fitting some 3W LED lights. With all the incredibly low energy lighting we use nowadays surely rating a lighting point at 100W is ridiculous and we could start fitting 3A MCBs (if available) for lighting circuits. Then everybody would be happy.
Wouldn't they?
 

Reply to Fusing Fans to manufacturers spec in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top