Currently reading:
Heating Wiring Problem - cylinder thermostat not working

Discuss Heating Wiring Problem - cylinder thermostat not working in the The Welcome Forum area at ElectriciansForums.net

If this was something I was asked to look at I would check the voltage on the control to the boiler (call for heating), I would prove the function of the boiler using a link between 3 and 4 I would prove be wanting to prove it was off when the link wasn't in place and that it fired up with the link. If not I'd call valiant and speak to there technical dept.

To prove the nest stat I would want to see the valves move. I think you can press the button on the controller to get it to call for heat. The arm moves on the side and I think it goes loose when energised.

To check the connections through the valves I would probe between earth and the orange from the valve in the energised and the de-energised positions. I'd only expect voltage on the orange core when the valve is open.
 
OK, so after finally finding a competent heating engineer, I though it could be helpful to share the solution!

Thanks @westward10 for temporarily reopening the thread!

Turns out the culprit was the Heating valve, which was faulty and sending a permanent live to the boiler, independently in which position it was on..

By replacing that valve, the issue was solved. (annoyingly a previous contractor had changed the HW valve - so the wrong one)

(Seems quite plausible in hindsight to be honest, but I guess it almost always is afterwards..)

The engineer also re-did the wiring from scratch, and with a rather clean result - please see below photos of all items.


Hope it is of help for someone out there! I'm definitely relieved to have a working HW and heating systems, before winter and those massive bills hit...

All the best
tsomek
 

Attachments

  • PXL_20220903_112616540.NIGHT.jpg
    268.6 KB · Views: 31
  • PXL_20220903_112746344.NIGHT.jpg
    472.7 KB · Views: 34

Reply to Heating Wiring Problem - cylinder thermostat not working in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock