Discuss Faulty Programmer /Diverter valve head/Wiring in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head as the heating was not coming on unless I had the hot water switched on as well, I then shut down the tank thermostat heating stayed on.
When the programmer was turned off the diverter valved stayed on H. I removed the power to the Central Heating and the valve returned to W under spring tension.
Tested:
No Power Valve on W
Power On - Call for Hot water on programmer, turned up tank stat and boiler fired up.
Call for Central Heating on Programmer, turned up room stat and valve moved to mid-position.
Turned down stat on cylinder and valve moved to H
Turned down heating and cylinder thermostats and valve stayed on H
Turned off CH and HW on programmer and valve stayed on H - i would have thought it should have restored to W under spring tension.
Remove power to central heating and valve returned to W.
I have a feeling there is a problem with the programmer. any one give advice - my brain hurts
Thanks
Ray
 
What exactly is the problem you are experiencing?

It looks to me like it is all working as exoected, assuming the boiler stops firing when all thermostats are turned down.
 
What exactly is the problem you are experiencing?

It looks to me like it is all working as exoected, assuming the boiler stops firing when all thermostats are turned down.
Thanks for replying, have done a bit more research on the valve _ Drayton Test Video for MA1 and as you say it seems to be working correctly, was concerned that the valve head was getting warm when turned off and sitting in the H position which I now understand is normal. Problem was that the heating would not come on when just calling for heating, had to start hot water as well.
Going to have a look at the diverter valve itself to see if it is not opening correctly.
 
Yes the valve will sit in the H position when when hot water is on at the programmer, the cylinder stat is satisfied and the heating then goes off. It is held in this position by the satisfied signal from the cylinder stat.
The valve head will get a little warm in this condition as the motor is holding it open.


When the hot water channel on the programmer switches off or the cylinder stat calls for heat the valve will spring return to it's unpowered state.
 
3 port valves are the devils work, why anyone fits one in a one off system I'll never know. 2x2 ports all the way, I can kind of get it if you are plumbing up a whole housing estate and you will save money on the number of valves. I wouldn't mind but you cant use a 3 port on a pressurised cylinder anyway, and if you do you have to fit a 2 port after it.
 

Reply to Faulty Programmer /Diverter valve head/Wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
439
Hi All. Its been ages since I have been on here- Fortunately log in details stored on PC. I have just had a new boiler and 210 ltr unvented tank...
Replies
9
Views
1K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
937
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock