Hi, having new hot tub installed, PME supply on 40A breaker 6mm twin clipped direct in loft down to 32A isolator, got some 10mm 2C laying around, and gonna use swa as earth from isolator will that be fine, (thought I’d ask not sure what these companies are like and I’m not around when they install so gonna lock off isolator and breaker and leave key for them)

Thanks
 
that's only 10A. usually fitted with a 13A plug and inline 10mA RCD.
 
I'd be breaking the earth on a PME and rodding down adjacent to the tub. 8 foot coupled rod. Small non-conductive four way external IP rated board with a 10mA and a 100mA s-type RCD in line. Rotary isolator mounted adjacent to the board. Take off a non-RCD way at the supply DB.

If you want a proper job that's the safest way to do it.
 

Reply to Hot tub supply in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock