Search the forum,

Discuss Insulation resistance query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
73
Was testing a 3 phase DB for storage heating. While testing I noticed I was getting continuity between 2 of the circuits, which were on separate phases. Each storage heater has its own 20A radial, and when doing an insulation resistance test between 2 of the circuits I get a reading of 0.00 ohms. I only get this reading between the 2 live cables, all other conductors are clear. Very strange reading to get, what are the chances of the 2 cables coming into contact and only the lives touching each other, or is there something I am missing?
 
i suspect that the heaters are switched on, you will continuity through the following links
heater 1 live to heater 1 N
heater 1 N to heater 2 N (common link)
heater 2 N to heater 2 live

therefore, continuity between heater 1 live and heater 2 live
 
So draw out your two circuits. Two resistive elements, a neutral from each to the neutral bar and the two live ends. You have a complete circuit.
 
But why only those 2 circuits? Why is this not the case with the other circuits, these were the only 2 circuits I had continuity between the live conductors
thermostats, switches, time clocks? any of them in circuit could prevent you from getting continuity through the circuit.
as westward suggests, draw out the circuit on a piece of paper and all will become apparent.
 
thermostats, switches, time clocks? any of them in circuit could prevent you from getting continuity through the circuit.
as westward suggests, draw out the circuit on a piece of paper and all will become apparent.
I understand why you would get continuity if the neutrals are still connected, through the elements. Just confused me as to why it was just they 2 circuits and none of the other 5
 

Reply to Insulation resistance query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
664
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
875
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock