Hi guys,

I've recently just completed a rewire of a small 2 bed bungalow consisting of 4 circuits. I have tested the kitchen ring and it has tested fine, the same with the lighting circuit. On testing the heating circuit and general ring main, the insulation resistance between L-N on both circuits is 0.3 Mohms. Between L-E and N-E they test fine at over 200Mohms. I have looked for the obvious i.e nails through cable in capping etc twists and kinks in cable. The cables move freely in the capping when pulled. The 1.5mm supplying the fused spur in loft for the heating is no longer than 6 meters in length. The general sockets however, I have split the ring down to find the leg which is causing the low reading and it seems to be the supply from the consumer unit to the first socket. But as I've said there are no nails, plaster, clips or anything on the cables. Really frustrating now, especially as the bungalow has just been skimmed!

Any chance it could be faulty cable?

Any help will be greatly appreciated.

Cheers
 
If your 'low' reading is L-N there will be a load connected somewhere......hopefully 500v up it's jacksie hasn't trashed it.
Usual missed culprits are heating controls,neons and tv amps. 0.3 megs is also typical of a surge protected lead.
 
If your 'low' reading is L-N there will be a load connected somewhere......hopefully 500v up it's jacksie hasn't trashed it.
Usual missed culprits are heating controls,neons and tv amps.

He says he's just rewired, so I assume he knows that there isn't a load connected! :)

OP, did you IR your cables before the plastering?
 
Heating is likely to be the Neon on the FCU.

With the socket circuit, disconnect both ends of the leg you think is the issue, if it is the leg that goes from c.u. to first socket (like you think) and still has poor reading - no other option other than to replace
 
Last edited:
He says he's just rewired, so I assume he knows that there isn't a load connected! :)

OP, did you IR your cables before the plastering?

Regardless...odds are if it's ok to earth it'll be a load. A real fault will almost always be to earth as the earth wire is between the live and neutral making a L-N fault without earth as well highly unlikely.
 
There are no loads connected and FCU's are non-neon. Basically just a 1.5mm up to a FCU with about a 6 meter length for heating, that's it, no combi fitted as yet. The property is completely empty.
 
The walls in contact with the cables mentioned are completely dry, they were plastered first before the rest of the bungalow last week.
 
100% nothing connected whatsoever, the heating goes straight from CU to FCU with no load (no combi fitted) and the first leg from the CU to the first socket also reading the same L-N, 0.3mohms
 
No the heating is directly from CU on its own circuit. The leg in question is the ring main to the rest of the bungalow. From the CU to the first socket, it's a reading of 0.3mohms L-N. From the first socket to the rest of the bungalow, it tests completely fine.
 
Hi guys,

I've recently just completed a rewire of a small 2 bed bungalow consisting of 4 circuits. I have tested the kitchen ring and it has tested fine, the same with the lighting circuit. On testing the heating circuit and general ring main, the insulation resistance between L-N on both circuits is 0.3 Mohms. Between L-E and N-E they test fine at over 200Mohms. I have looked for the obvious i.e nails through cable in capping etc twists and kinks in cable. The cables move freely in the capping when pulled. The 1.5mm supplying the fused spur in loft for the heating is no longer than 6 meters in length. The general sockets however, I have split the ring down to find the leg which is causing the low reading and it seems to be the supply from the consumer unit to the first socket. But as I've said there are no nails, plaster, clips or anything on the cables. Really frustrating now, especially as the bungalow has just been skimmed!

Any chance it could be faulty cable?

Any help will be greatly appreciated.

Cheers

How have you done this of the job has been plastered?
 
Because the cables move freely in the capping, I have also managed to pull the leg out from CU to first socket and there's is no physical damage at all.
 
Yeah I will when I go back tomorrow, I'd just had enough after trying to get my head round why both cables would show the exact same fault L-N when they're not even from the same drum and different size.
 
Something ain't adding up here mate, as dill said if you have identified what leg it is then what's the problem or am i missing something ????
Surely as you did the wiring you know all routing of cables you would be in a good position to sort it.
Im not sure i can add anymore to the advice already given tbh.
 
Yeah I have identified the leg and will sort it but as I said, I just thought it was slightly weird how the heating supply and first leg had identical issues that's all, that's why it was confusing me and wanted a second opinion.
 
Yeah I have identified the leg and will sort it but as I said, I just thought it was slightly weird how the heating supply and first leg had identical issues that's all, that's why it was confusing me and wanted a second opinion.

Hum, that does sound a bit of a head scratcher. Have you tested for continuity between both sections of cable?

Please do update the thread with what you find.
 

Reply to Insulation Resistance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
650
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
779
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
975
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
315

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock