Currently reading:
Intermittent Fault - 20 characters

Discuss Intermittent Fault - 20 characters in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

H

hightower

Been having an intermittent fault at home now for a few months. All RCBO board, wiring 3 years old.

Upstairs socket RCBO trips sometimes, maybe once or twice a week. Always seems to be when we turn something on, for example a light, cooker hood, oven etc. I'm thinking there's a dodgy appliance on the upstairs sockets, probably an extension lead, that's creating an intermittent N-E fault. Haven't tested anything yet, I'm sure you all know how it is with jobs at home... I think I'll be beginning with a PA Test of appliances when I get time, but just thought I'd post up here to see of any theories?
 
Have you checked the connections at the RCBO?

Can you leave most of the items unplugged?

Got any water leaks?

Hung any new pictures recently?

Have you ramp tested the RCBO?

Have you ir'ed the circuit?

Have you clamped the tails?

Is the kettle working?
 
Something this is permanently plugged in is almost certainly creating a permanent leak, not enough on its own to trip the RCBO, then when another device which also on its own isn't enough (and even cumulative with other similar devices) wouldn't normally cause the RCBO to trip, is not enough to push it over.
You could do an IR test across the circuit with everything that can be safely left plugged in and then work through socket by socket.
 
I've been putting it off because I know it's not gonna be a ten minute job. I even have an inkling what's causing it - an extension lead that is plugged in behind a massive bed that needs dismantling to get at. Oh well, job for the weekend, or maybe even bank holiday weekend since it'll be raining then by default anyway.

I'll update the thread when I do get round to it, but don't hold your breath
 
Pat testing isn't a bad start to try figure it out.

I'd take note of when the fault happens, certain time?

We've had it before where it was the moulded plug and lead to a cooker hood. Obviously found this after squeezing in cupboards to look behinds sockets :(
 
Pat testing isn't a bad start to try figure it out.

I'd take note of when the fault happens, certain time?

We've had it before where it was the moulded plug and lead to a cooker hood. Obviously found this after squeezing in cupboards to look behinds sockets :(
It's not happening at a particular time but I did suspect the cooker hood initially. Time to get motivated and begin testing
 

Reply to Intermittent Fault - 20 characters in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top