Is this installation considered acceptable today? (1-ring including oven and everything else)

Discuss Is this installation considered acceptable today? (1-ring including oven and everything else) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
23
Looking for some advice on what I've discovered is the electrics situation in my rental property.

I'll note that before I moved in here I made the Letting agents (LA) more than aware I use an absolute -----ton of power. I told them I can and will be pulling 2,000-4,000 kWh a quarter (with gas hob and heating). No concerns raised.

When I moved in here it looked promising. CU had no spare slots, plenty of MCBs and RCD protection in place. Nice one I thought, 4x 32A MCBs, good chance we've got a couple of rings and kitchen will be on its own. As it turns out, nope.

I haven't removed the cover, so I have not been able to confirm what connections we have inside the CU but I can confirm my findings in terms of what the resulting circuits are.

1) 16A - Does nothing
2) 16A - Radial to water heater switch, on to a switch in the living room that's got a single GU10 lamp installed in a unit coming from it. (Water heater removed some time ago)
3) 6A - Smoke alarms [Issue: One not receiving mains power but clearly wired into the trunking containing this circuit so should be]
4) 6A - Lights (Kitchen, Bathroom, Master Bedroom)
5) 6A - Lights (Lounge, Hallway, Second bedroom)

So far so good, this looks great, other than the oddity of feeding the GU10 lamp from the previously installed radial, but makes sense as this terminates inside the bottom of the unit containing the GU10 so just laziness prevails.

6) 32A - Does nothing
7) 32A - Does nothing
8) 32A - ALL sockets (Lounge, hallway, kitchen, oven, boiler, master bedroom, second bedroom)
9) 32A - Shower
10) 40A - Does nothing

Not so good. We have a single 32A ring covering everything including the bloody oven, washing machine, tumble dryer and the rest of the gaff on top!

Why the hell install all of those 32A MCBs to do sweet F all?

I've confirmed this is definitely the case by killing off the circuits in almost every possible order and I can see that nothing else is getting a complete circuit to these circuits enabling power to flow.


Now for the big question.

I did some maths here and it looks like this is seriously overloaded pretty much any time we're using the kitchen pretty heavily (most nights...).

A typical evening in the house consists of washing and drying lasting 3-4 hours, concurrently (4.6kW total), whilst over the course of this the oven will be put on (7.8kW total) and often a hair dryer (8.8kW total) and kettle (11.8kW total) too. Admittedly the last two are far shorter use, but this is seriously over the rating for this circuit and I don't feel it's over the top usage of a house.

Let's add up purely the kitchen during a typical wash and prepare meal:
2,550W - 3,000W - Kettle
900W - Toaster
80W - Fridge
125W - Boiler
2,200W - Washing Machine
2,400W - Tumble dryer
3,200W - Oven

Not all of this will be on all the time but lets assume this is peak before taking into account any of the rest of the property.

11,455W or 11.45kW best case, 11.8kW worst case. Now my 32A circuit should not be over 7.2kWh and probably not over 5.76kW for extended periods.

Then we get to two HDR tellys on pretty much all the time, set top boxes, server, multiple PCs with multiple monitors connected, PoE Switches and networking gear, smart home gear and when I am using it I often have a lab set up with multiple PCs which is where we get to the 4kW/quarter.

Right now, I'm concerned that before we even cover the devices used throughout the house, the kitchen alone (well counting the hall cupboard with tumble dryer) is pulling 159% - 164% of the rated load on this circuit.


I know that the best practise for a single ring can be based upon property size, not certain of the specs here though.

I'm unsure of the sq footage of the entire property but I'd say it isn't particularly small. We're looking at 165 sq feet in the master bedroom alone.

Should I be raising this with the LA and pushing to get this sorted out so that at very least the oven is moved to its own radial circuit and preferably get the rest of the kitchen moved over to its own ring too?

Would you suggest it's worth myself looking at spurring off this 16A radial to get an extra couple of sockets, capable of at least 13A, running in the living room that won't be on this single ring?

The 32A to the shower is currently running into the hall cupboard where there is an isolator switch. The sockets in there are on the main ring and contain my comms cabinet and the tumble dryer. The comms cabinet won't use a huge amount, although does have quite a few devices and PoE switch providing power to WiFi, VoIP phones and some smart home devices. Is there anything I could do to take power off this? Either going with a fused spur or a Garage CU that then splits into the shower and extra sockets? (I know this will require notification and a competent installer doing it).


Any thoughts from the pros would be greatly appreciated here as I'm not sure if it would be considered enough of a problem to have a LA take action, however, way I see it I'm constantly stressing this system beyond what it was intended for with no idea how the wiring quality in the walls is, so it's a concern, whether or not the LA will do anything or not I'm not sure and I don't want to raise it without getting some professional opinions.
 
Good to know, so that signal is not going to be even close to WiFi - and longer range which makes sense for safety devices.

I found the WiFi to be dire even before the CCTV got added in, but it definitely adds strain to it!

The solution I came to was to put an AP in the lounge and an AP in the master bedroom, pretty much opposite ends of the house, and it works pretty well.

If I continue to have issue, may split the network for the CCTV and the rest, but I'm in the process of running 12x CAT6 to each room so the WiFi really is non critical for anything intensive by the time I'm done.

12 CAT5 points in every rooom - bit of an over kill ...
 
40 minutes is a bit quick... even though theres 2 of them, and the number of circuits in the CU is quite small.... they must be really experienced in doing EICR's that they can do them in such a quick time.:rolleyes:

So its proved there is, and has always been only 1 ring final circuit here for all the sockets in the house.

So what is it with all the IT equipment? Either large scale pirate bluray copying going on or editing of some rather "specialist" films?:eek:
 
In my view that is commercial scale use of a domestic supply "technicalities" aside, to put it another way it is not normal domestic use of a system designed for exclusively domestic use. If I were a landlord and the system was overloaded by your use I would be looking to you for reparations. The onus would be on you to rebutt the claim. But as has been stated it is highly unlikely you would overload the system anyway. Bear in mind there have been tenants before you and evidently there has not been a problem, if there is in your particular case it may be that you are using the system in a non normal way.

12 CAT5 points in every rooom - bit of an over kill ...

Cat6 man. Not a huge difference but it has that plastic down the middle which helps to separate the pairs achieving up to 10Gbps instead of up to 1Gbps on Cat5E, or longer runs at 1Gbps.

It also helps with interference when running a lot in close proximity, which I definitely am.



The reasoning behind so many ports per room (or at least master bedroom and lounge) is that I want every single device back to the central comms cupboard where I have two 24-port managed switches which I can set up VLANs (virtual networks) on and segregate things.

For example, all my VoIP phones are on one network but they can't speak to the PCs. The entertainment stuff (Xbox, Apple TV, etc) can speak to the PCs to stream, but PCs can't directly access them because they don't have to. Guests on WiFi can't communicate with the wired network. Etc.

I've also got specific colour patch leads for each thing, black for PCs, red for media, blue for PoE, etc.

Over the top in terms of set up and organisation but I like it.
 
40 minutes is a bit quick... even though theres 2 of them, and the number of circuits in the CU is quite small.... they must be really experienced in doing EICR's that they can do them in such a quick time.:rolleyes:

So its proved there is, and has always been only 1 ring final circuit here for all the sockets in the house.

So what is it with all the IT equipment? Either large scale pirate bluray copying going on or editing of some rather "specialist" films?:eek:

Oh no, as far as I can ascertain they have not actually completed another EICR. I asked my LA if they're going to need to have this re-done.

I work in IT mostly doing network design, implementation and deployment; and software development, so I've got various operating systems and machine specifications here for testing.

I'm also quite interested in performance testing and for that you need to simulate high processor or graphics usage for long periods and try to tune around it.

I am also quite partial to security testing so firing up a lot of graphics cards to try and crack a password hash, which when running for hours or days on end can push 300-400W per graphics card. 1,500W PSUs getting pushed to 100% is not uncommon, however, that can actually toast the 3-pin sockets so I prefer to use up to 1,000W per PSU.
 
I'd like to thank everybody here for all of your responses!

I really, really, do appreciate all of the time and effort you've taken out of your day to provide excellent information and advice.

Just FYI, I've discussed my set up with the electricians out today and I think the conclusion will be running a radial or two for my set up and they're fine with me providing the materials and running the circuit.

They may not let me terminate into the CU myself even with them present, will try my luck, but certainly I'll get some experience out of the design and installation of a proper circuit, albeit achieved with trunking.

Hopefully any further queries I have will be of a more technical nature with me demonstrating some knowledge and not just being a noob.

Thanks again.
 
New posts

Reply to Is this installation considered acceptable today? (1-ring including oven and everything else) in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top