Issue with cat 6 connection

Discuss Issue with cat 6 connection in the UK Electrical Forum area at ElectriciansForums.net

Sb8389

-
Reaction score
25
Hey guys
I installed a cat 6 ftp cable last week around 50metres. It goes from one cat6 faceplate to another. When I originally tested the connection it was fine with my network tester,we tested with a couple of cat 5e patch leads to check connectivity and was fine. Today the customer has brought a couple of cat 6 patch leads and re tested (getting no connection). I popped out tonight and tested the line with my tester and getting nothing, would you point towards it being a module issue as the tester would pick up open circuits so I know it’s not that.
From your experience what would you guess it could be.
 
Check the patch leads to see if they are standard cables or crossover leads and check each cable separately whilst disconnected.

What tester are you using as I used to use a Fluke Link Runner for integrating cable runs and port locations.

FLUKE NETWORKS LinkRunner AT 1000 Network Auto-Tester - The fastest... - https://www.comms-express.com/products/linkrunner-at-1000-network-auto-tester/
Bit more advanced machine than the philex network tester from Screwfix pal haha I shall check the cables when I go back. Thanks for the advice
 
Quite informative PEG, what 28 continuity tests would you carry out to ensure all is ok.
These
Continuity testing data.jpg
 
I had a similar problem,it worked,then weeks later failed.
I changed the data module,re connected,& ok....fingers crossed.
Don’t know about you,I kinda loose it a bit on these connections,not really knowing the in’s & out’s.
 
Quite informative PEG, what 28 continuity tests would you carry out to ensure all is ok.

Hi,i would have carried the most basic of tests,using whatever AVI or resistance measuring device i had to hand,and would have an indication,before i had tea,whether or not it was O/C on one or all conductors.

Before i did the above,any multi-continuity or TDR type testing,i would do the following....make sure,i had the two ends of the same cable,EVEN if i fitted it initially...i would walk the route,giving every inch,a good,hard Paddington bear type stare,to look for clues.

I would be assuming the worst - and then discounting it.

....Maybe someone pulled a t&e,through one of your holes/conduits....maybe it was tight,and they pulled back and forth,and sawed through your cable,and now,one of the live conductors,is bridging or has severed,the CAT cable...

It is unlikely,but can happen,as i have seen it happen,so get stuck in,be thorough,be successful,maybe even be a hero....but sort it,invoice accordingly and then..........relax:cool::)
 
Is
Hey guys
I installed a cat 6 ftp cable last week around 50metres. It goes from one cat6 faceplate to another. When I originally tested the connection it was fine with my network tester,we tested with a couple of cat 5e patch leads to check connectivity and was fine. Today the customer has brought a couple of cat 6 patch leads and re tested (getting no connection). I popped out tonight and tested the line with my tester and getting nothing, would you point towards it being a module issue as the tester would pick up open circuits so I know it’s not that.
From your experience what would you guess it could be.
Is it installed in containment throughout its length? This is important with data cables.
 
Not completely no, it possibly has around 5metres where it aint possible to install containment so just clipped, what affects could this have on the cable?

It's about the potential for damage to the cable.

There is nothing wrong with an exposed cable per se, although I would be cautious about running one where it was exposed to UV from the sun on a long term basis.

It is easy to damage a data cable by using inappropriate cable clips. In particular, the use of plain wire staples (as favoured by BT for telephone wiring) is not generally recommended as it is difficult to avoid over-driving them, resulting in putting a nasty kink in the cable. This matters a lot for CAT5 and it is even more crucial that it is avoided for CAT6. The longer the run the more important it is that the integrity of the cross section of the cable is not altered at any point and again, whilst important for both types, this is more crucial for CAT6.

It is also very easy to permanently screw up a network cable by pulling it around bends in conduit and the like using force which would not cause the slightest problem to a bit of T&E.

Having said all that this pertains to data integrity and not OC conditions.

For OC I would be looking for a severed cable. It's not impossible but highly unlikely to induce an OC in all 8 cores but in order to do that some major thuggishness would have had to have been deployed in the original running of the cable and the defect would likely have been immediately detectable.

Punch down faults tend not to affect all 8 cores, so I would again be looking for a cut in my cable. it has been noted that the correct form of punch down tool is deployed and this is true. it is, unfortunately, certainly also true that if one tries "hard enough" it is possible to apparently achieve a connection using the wrong tool but it will be very unreliable and liable to fail at any point in the future. Once again though, this happens on a core by core basis, so if you have (had) continuity on the original install and now have none on all 8 cores then it is not likely (although not absolutely guaranteed to be impossible) to be either a punch down or a module issue but a wholesale break in the cable.

It's an Occam's Razor thing.

No continuity on any core? You're looking for serious cable trauma.

Just lost one or two cores? Consider punch down failure, module failure (it doesn't do to cheap out on quality of the component here - especially for CAT6), or cable trauma but less severe than above. This last can be a real sod to find visually, as trauma sufficient to break a single core can be very difficult to spot by eye. Easy to spot with a resistance / continuity check of course and typically is going to require that you strip out and bin the original cable in it's entirely anyway, as patching in new sections of CAT6 cable to replace any physical damage is not recommended from the POV of guaranteeing the data integrity (i.e. speed).
 

Reply to Issue with cat 6 connection in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top