Discuss kva for a flat with all electric heating in the UK Electrical Forum area at ElectriciansForums.net

UKPN came back to me and said they could supply 23kVA by routing from another source without additional cost so am going with that.
I got a quote from them and ma now looking to find someone to do the contestable stuff. UKPN are very slow and the quote seems a lot.

Can anyone recommend a contractor that can do this kind of stuff in South London?
thanks

Hi Gus,

This thread has been very interesting. I am in a similar situation. I have a large house that is being converted to 4 x 1 bed flats for young professionals plus a landlord supply. That means 4 x dishwasher, washer/dryer, induction hob, electric oven etc. I also want the landlord supply to be enough to allow for an electric car charge point in the future. I also want to plan for the fact it's looking like gas boilers will be phased out in favor of electric within 10-15 years.

My spark came back and said each flat would have an 80Amp (AD) demand based on appliances and that 100Amp would be ideal given lighting, plugs etc So 23Kva.

5 x 23Kva = 115KVa

My next question is that Ryefield boards are designed to sit on a 100Amp supply (at least the ones I've looked at). A 115KVa supply would exceed this, no?

UK Power really need to do a dummys guide 101 on this.

Asking as a property owner/non-spark.
 
Hi Gus,

This thread has been very interesting. I am in a similar situation. I have a large house that is being converted to 4 x 1 bed flats for young professionals plus a landlord supply. That means 4 x dishwasher, washer/dryer, induction hob, electric oven etc. I also want the landlord supply to be enough to allow for an electric car charge point in the future. I also want to plan for the fact it's looking like gas boilers will be phased out in favor of electric within 10-15 years.

My spark came back and said each flat would have an 80Amp (AD) demand based on appliances and that 100Amp would be ideal given lighting, plugs etc So 23Kva.

5 x 23Kva = 115KVa

My next question is that Ryefield boards are designed to sit on a 100Amp supply (at least the ones I've looked at). A 115KVa supply would exceed this, no?

UK Power really need to do a dummys guide 101 on this.

Asking as a property owner/non-spark.

Off the top of my head that seems like a very high demand for each flat.

Ryfield boards are normally designed to be supplied at a bit more than 100A, they usually have 100A rated outgoing ways.

Nobody is going to produce a dummies guide because it is a technical subject and involves well established scientific principles and calculations, without learning this and gaining experience working alongside those who are experienced at it you can't get it right.
There are too many variables and considerations to reduce it down to a simplified guide.
 

Reply to kva for a flat with all electric heating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
822
Hello everyone! I have a question regarding the electricity supply and the maximum demand. One energy utility supplies an 18 kVA maximum...
Replies
10
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
806
In July I moved into my new home with Schluter DITRA heated floors in the bathroom. The floor quit working in December, and my GC and a rep from...
Replies
0
Views
343
I'm hoping somebody can help me. Im converting a 4bedroom flat to 3 x 1bedroom flats. I am having a new 3 phase supply installed for 3 the...
Replies
19
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock