Discuss LED High bays flashing!! in the UK Electrical Forum area at ElectriciansForums.net

dlt27

-
Reaction score
26
Hi all, any advice would be greatly appreciated.
Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed 20 400w metal halide to 150w LED high bays). The florries were fed from different circuits and different DB’s and the high bays were fed of one DB, but from different phases and through contractors. When changing the florries I noticed there was a tiny spark when the neutrals touched any earth. I measured between N and E a few times ant different fittings and all I got was 3v on the fluke so not borrowed neutrals. I thought it might be to do with imbalance of the phases, but not totally sure!
When I changed the high bays ( click roses so didn’t have to kill anything) they worked fine for two days, but today I got a call saying a couple had started to flash/ pulse. At first one did it for 2 hours then stopped then a different one started and stopped and by the end of the day they said 3 were doing it… All ZS’s for circuits were fine..
I just wondered what everybody thoughts were and what to try? Could it be a lost neutral?
Thanks again for any replies..
 
I had something similar on some warehouse flories a few years back, all was fine until load was put onto the system and they started dropping out. Cause was a broken neutral compounded with a neutral to earth fault.
 
I had something similar on some warehouse flories a few years back, all was fine until load was put onto the system and they started dropping out. Cause was a broken neutral compounded with a neutral to earth fault.
I’ve got a feeling it’s something to do with neutrals, however the loads been reduced because swapped 400w for 150W LED’s. Original 400w high bays were fine.Thanks
 

Reply to LED High bays flashing!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
8K
Hello, I've installed a Monsoon Extractor Fan kit today, all is up and running and everything is working with the exception of the LED. When I...
Replies
0
Views
697
I really need help with this puzzler. First - I am moderately 'skilled' in day-to-day basic wiring. My puzzle: I am trying to replace a...
Replies
10
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi I have a 3phase shop in a high humidity area in (Hawaii) and I'm having some issues with low voltage on the single phase outlets on the 120v...
Replies
6
Views
886

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock