Yes, mostly they are 10% or even 20% tolerance.Just measured it. It was 95NF so 5% less than it's rated farad which I'm guessing is fine?
Discuss LED light in bathroom flashes when extractor fan TP pole switch is closed. in the UK Electrical Forum area at ElectriciansForums.net
Yes, mostly they are 10% or even 20% tolerance.Just measured it. It was 95NF so 5% less than it's rated farad which I'm guessing is fine?
So any thoughts on why the snubber did not work in this case. Would you then need more than 1 snubber or a different rated one?Yes, mostly they are 10% or even 20% tolerance.
No, it did absolutely nothing. Thanks for all the input pc1966Did the snubber change anything?
Some DC leakage by a controller would not be shunted off by a snubber, so this might just be a reason for it.
Reply to LED light in bathroom flashes when extractor fan TP pole switch is closed. in the UK Electrical Forum area at ElectriciansForums.net