Papawhitt

Hi Guy's, im looking for a little professional guidance,

I have recently replaced my kitchen lighting from compact fluorescent and GLS lamps with LED down lights and strips.
Both switched from a double wall switch, single pole.
The entire down stairs lighting circuit is protected by a MEM M6 Type 1 5A RCD.
The down light circuit is on one switch and the LED strips on the other.
The down lights do not cause an issue.
The strips trip the RCD approximately 5 times out of 10 on switch on, however if the light switch is left in the on position the RCD resets with no re-tripping and the strips operate with no other problem.
The total wattages are both much lower than the previous lighting circuit.
I have checked each strip for short circuit but all operate perfectly on there own.
I am thinking the 12v constant voltage drivers are causing a spike/In rush?
would changing my RCD be the answer?

I thank you in anticipation of your assistance

Best regards

Papawhitt
 
Hi,

Firstly, from your description, I think you're referring to an mcb (miniature circuit breaker) rather than an rcd.

The problem sounds like it is inrush current on start up. You have said that it's a type 1 breaker which could possibly be changed by a type 2 of the same value. However, the circuit would need testing by an electrician first to ensure that a type 2 device would be suitable. The only problem is that the old M6 breakers are obsolete so you may have to source one second hand.

Best advice is to get an electrician to have a look.
 
I appreciate your quick response and advice, thank you very much

Hi,

Firstly, from your description, I think you're referring to an mcb (miniature circuit breaker) rather than an rcd.

The problem sounds like it is inrush current on start up. You have said that it's a type 1 breaker which could possibly be changed by a type 2 of the same value. However, the circuit would need testing by an electrician first to ensure that a type 2 device would be suitable. The only problem is that the old M6 breakers are obsolete so you may have to source one second hand.

Best advice is to get an electrician to have a look.
 
Hi,

Firstly, from your description, I think you're referring to an mcb (miniature circuit breaker) rather than an rcd.

The problem sounds like it is inrush current on start up. You have said that it's a type 1 breaker which could possibly be changed by a type 2 of the same value. However, the circuit would need testing by an electrician first to ensure that a type 2 device would be suitable. The only problem is that the old M6 breakers are obsolete so you may have to source one second hand.

Best advice is to get an electrician to have a look.

Yes.

I've changed drivers on LED strips to ones with lower inrush. I tested the 24V constant voltage ones from this range and found them to be well behaved:
Electronic Components/Optoelectronics/LED Drivers | Rapid Online
 
Two things that immediately spring to mind. Firstly the LED light strip drivers probably have internal surge arrestors. When surge arrestors actually 'arrest' a surge it would be seen by the RCD as a fault current.

Secondly the RCD is supplying other circuits and the earth leakage it sees is the cumulative leakage of all those circuits simultaneously. Consequently if there's already a reasonably high amount of standing leakage on the other circuits even a small amount of extra leakage introduced by the LED drivers might be enough to take it past the tripping threshold.

You need special test equipment to check leakage currents and it's very expensive so the only way you're going to 100% resolve this is to get some help from an experienced sparky.
 
Thank you for your reply,the problem is a little more complexed than I thought, I am not even going try and say I understand the principles of earth leakage.
However I am having my bathroom renovated in a couple of weeks and my fitter contracts out the electrical work so i will run my problem past the sparky when he comes
 

Reply to LED lighting tripping RCD in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

We have one room that seems to have lost most of its power last night. One of the outlets in the rooms has a power strip plugged in that powers...
Replies
5
Views
808
Wanting to add 2 strips of led lights down each side of underneath of the stairs, I have a socket I can spur off, into a fused switch, been...
Replies
1
Views
830
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
707
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
429

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock