Currently reading:
Lightning Protection Noise on earth rod

Discuss Lightning Protection Noise on earth rod in the Australia area at ElectriciansForums.net

S

sparky1690

just been spammed with testing an installations Lightning protection system out in Afghan. was installed nearly a year agbo but the lad that installed it has now done one so i get the honour of testing it.

it has two sets of cabins each with 8 earth pits around them, the rods are not linked below ground, some of which are inaccessible now because of walkways etc. :mad:

i only have a fluke clamp meter as my megger is away for calibration so getting in to the pits to try & test is a no starter.

when i measure the down tapes i am getting the noise symbol on the test meter & when refered to the instructions makes the result void. this does not happen at every down tape only around half of them. the others pass but only just, around 9 ohms.

any ideas on how i could rectify the problem short of digging trenches & ensuring they get some sort of farraday cage type effect.

cheers.
 
Last edited by a moderator:
I would start by checking all the connections above ground for corrosion and tightness, and hope to find something.
I've only used the clamp on meters a few times, but I have found when testing indvidual spikes with a standard meter it's pays to use the rest of the installation as your test electrodes, that way poor connections above ground show up.
 
Is the lightning protection connected to the main earthing terminal or seperate?
Is it possible to isolate the power to the cabins, and then try?
I'm guessing it's all generators out there, if so are they close to the installation?
 

Reply to Lightning Protection Noise on earth rod in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock