But how is that the Watt/hour meter (I mean the meter which supplies data for consumption charging purposes to the energy supplier), is driven, at the supply voltage and frequency, by only real power?

Is it because the current which is the basis of the apparent power is out-of-phase with the current basis of the real power?

If so, why does the power developed by the out-of-phase current not do work in the meter's current coils?

The watt-hour meter (not watt/hour. that's watts per hour) performs real-time vector multiplication of current and voltage to resolve only the in-phase, real power component. In a traditional spinning-disc meter this is done magnetically by the interaction of the two fields set up by the voltage and current coils. Only the in-phase component of the field created by the current coil generates nett torque on the disc. In a smart meter the same multiplication is done electronically.

It is equally possible to arrange the meter coils to register only the reactive component. Both instantaneous kVAr meters and kVAr-hour meters are used on industrial supplies to monitor reactive power flow, because this is chargeable on large consumers' tarriffs. Not as energy supplied, of course, but to defray the cost of installing oversize transformers and cables to carry the reactive component of the current that does not pay for itself with energy supplied. Chargeable reactive power incentivises customers to maximise their power factor, i.e. minimise the current needed to supply their real power demand.
 
The watt-hour meter (not watt/hour. that's watts per hour) performs real-time vector multiplication of current and voltage to resolve only the in-phase, real power component. In a traditional spinning-disc meter this is done magnetically by the interaction of the two fields set up by the voltage and current coils. Only the in-phase component of the field created by the current coil generates nett torque on the disc. In a smart meter the same multiplication is done electronically.

It is equally possible to arrange the meter coils to register only the reactive component. Both instantaneous kVAr meters and kVAr-hour meters are used on industrial supplies to monitor reactive power flow, because this is chargeable on large consumers' tarriffs. Not as energy supplied, of course, but to defray the cost of installing oversize transformers and cables to carry the reactive component of the current that does not pay for itself with energy supplied. Chargeable reactive power incentivises customers to maximise their power factor, i.e. minimise the current needed to supply their real power demand.
 
The watt-hour meter (not watt/hour. that's watts per hour) performs real-time vector multiplication of current and voltage to resolve only the in-phase, real power component. In a traditional spinning-disc meter this is done magnetically by the interaction of the two fields set up by the voltage and current coils. Only the in-phase component of the field created by the current coil generates nett torque on the disc. In a smart meter the same multiplication is done electronically.

It is equally possible to arrange the meter coils to register only the reactive component. Both instantaneous kVAr meters and kVAr-hour meters are used on industrial supplies to monitor reactive power flow, because this is chargeable on large consumers' tarriffs. Not as energy supplied, of course, but to defray the cost of installing oversize transformers and cables to carry the reactive component of the current that does not pay for itself with energy supplied. Chargeable reactive power incentivises customers to maximise their power factor, i.e. minimise the current needed to supply their real power demand.
I agree that Watt/hour is not correct. It is Watt-hour (or Watt hour).

My mistake arises from" /" interpreted, very reasonably, as "per".

One Watt-hour is one Watt of energy exerted over a duration of 1 hour. 1 Watt PER hour suggesst a continuing power of 1 Watt for one hour and for each subsequent hour.

Thanks for picking me up on the sloppiness!

And thanks for explaining precisely why the Watt-hour meter is driven by only by in-phase current (x Volts).

I guess, sooner or later, that domestic consumers will also be charged for total power, depending on the p.f. of their installation. Inductive devices multiply "exponentially" (may not be a totally sloppy term here!), and not necessarily just ones with tiny power ratings. LED bulbs are no better than fluorescent tubes (in p.f.), and are worse than latter with electronic ballasts, but, fortunately, consume much less current per lumen emitted.

All very interesting, and illuminating!
 
Last edited:
one Watt of energy

Did you plant that for me?
Power / watts
Energy / kWh or joules

Sorry, but I know you know what you are talking about fundamentally and can't let you get away with it :)
 
Oh, dear, another boo-boo! I didn't plant it. I wouldn't be so foolish!

Yes, I see my error! The Watt hour (Watt-hour) is the unit of energy (so what is the Watt on its lonesome?)

We are dealing with a relationship between force and power very like that (torque and power (work)) in engines/motors which exert a rotating force, and develop power, and so perform work, over time and distance.

This explains why the Watt has fairly recently become a common unit for work done, but it's just plain Watt without specifying the time/distance over which the underlying force is exerted. As you will know, It originates in the differently named unit that James Watt devised to persuade farmers to swap their horses for a Boulton and Watt one or two horse-power static steam engine.

That old unit has stuck. You still rarely find even aware motorists quoting engine power in Watts, and the same is presumably true where they don't call a horse a horse (eg, Germany, France, Italy).

THOUGHT

I still don't know what to do to estimate reasonably reliably the peak power consumption of our single-phase circuit. The monitor which I found proved unsuitable for long-term monitoring, and the same seems to apply to the two suggested by our good friend Avo.

Do you have any suggestions - apart from a LOT of very wearisome, and probably inaccurate, counting and adding up?!

All the best,

Carl
 
Do you have any suggestions - apart from a LOT of very wearisome, and probably inaccurate, counting and adding up?!
I think I have a slightly clearer idea of your requirement now. I was focussed on PF before, but for kWh there do seem to be a few products out there.

Here's one which uses a current transformer connected to a 'hub', that uploads usage data to their platform. You interrogate the data on your phone/ tablet/ laptop, and can download accumulated data (In CSV format if you want to play with it in Excel!)
I haven't looked at this in detail, so may still not be suitable. I see the current transformer 'dongle' is battery powered, but I suspect those batteries should last a good time, say 6 months or a year?


There are also professional data loggers from Fluke etc, but I was concerned both the cost of the hardware plus software licensing might make such equipment prohibitvely expensive.

PS. I'd just buy the £18 display, see what the figures look like, including PF, and if happy with the outcome (!), proceed with the logger above. It's only money 😃
 
Last edited:
Thanks very much.

I will have a look.

You'll be surprised to hear that I don't have any experience of CSV format. I have looked up what this is, and don't feel much the wiser!

I don't have Excel installed on my PC, because I don't pay for MS Office, but I DO have LIbreOffice, which includes a spreadsheet program similar, I suspect, to Excel.

But I've never used it because I like a manual to consult when writing a spreadsheet, and, to my knowledge, there isn't one for LibreCalc. Possibly there is a "Dummies" manual, If not, I would have to keep looking elsewhere on line while working to find out how to operate this program smartly.

Would I be able to load data downloaded from the logger in CSV format into LibreCalc, do you think? I believe the free program is a clone of an unlatest version of Excel.

I create spreadsheets for various purposes quite frequently. I use a brilliant very old spreadsheet program SuperCalc5. It's only shortcoming is the limited memory that it is able to apportion to a single spreadsheet, but, so far, I've not found this a problem in practice.

It's a DOS program, so won't run in any version of Windows after XP, and it can't intercommunicate with any Windows program, or email.

I started using SuperCalc on our first computer, an Amstrad, in 1987, and have stuck with it in PC format (the last version being 5) since.

So how can I be able to use it when my PC runs Windows 10?

I have a Windows 98 computer. and a Windows XP one, where it is installed and usable. But, ironically, it runs best, and prints fastest, in my version of XP installed as a virtual machine within Oracle Virtual Box on the hard disk of my W10 machine. Although SC5 can print only through a parallel printer port, and these are now long defunct, I run an Italian software program that enables DOS programs to print through a USB port.

Curiously, although SC5 runs better in XP VM than in real XP, the memory size is still limited, as dictated by the program. But, also curiously, the program apportions a larger memory when it is running in XP VM than in XP itself.

Could I load CSV data from the logger into LibreCalc? I think that this program is a clone of an old version of Excel.

As already mentioned, I've never dealt with data in CSV format, so this would be a new learning experience!!
 
.Could I load CSV data from the logger into LibreCalc? I think that this program is a clone of an old version of Excel.

As already mentioned, I've never dealt with data in CSV format, so this would be a new learning experience!!
Yes you could.
Libre Calc guide here:

It's much simpler than it sounds, especially after you have done it a few times!
 
Last edited:
Fuse responds to the VA load, real and apparent
Thanks again for your help, and your very interesting account of the gshp job. Hope the over-heat problem has been sorted by the designer/supplier.

I did ask you who you would suggest to size up the feasibility of gshp for our own home. That question probably got buried under the other issues, but, if you can spare the time, I'd appreciate a lead. It would seem that a firm specialising in the remarkable Stiebel pumps that you described would be a good starting point.

Here's hoping for a suggestion made with the benefit of your experience of the market.!

All the best,

Carl

PS thanks to various contributors, yourself among them, I now know for sure that the supply fuse load is the kVA h of the the supply, not the kWh. And I also now understand why this is, counter-intuitive though it first seemed to me!
 
The process works something like this:
1. Choose a GSHP installation company. ( DM if you want a suggestion for your area)
2. Said GSHP installation company will have knowledge, experience and service from their chosen GSHP manufacturer, e.g. Siebel (there are many others)
3. Engage said company for a design, this will generally be backed off to the manufacturer, e.g. "Install Co" backs off design to "GSHP Manufacturer Co"
4. Based on your local environmental conditions, e.g Land Area, soil type, availability of ground water, the manufacturer of the GSHP will design the ground loop.
5. Install Co then installs to GSHP manufacturers design -

Hope this helps and glad you are in sync with the electrical engineers nightmares of dealing with the plethora of AC electrical loads and its impact of current carrying infrastructure (and we have not even mentioned harmonics yet), lol
 

Reply to Load in Amps on a mains single-phase circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. This has always got me confounded. Witha 4-pole 63A breaker, can someone please confirm/advise what the current carrying capacity of...
Replies
14
Views
443
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
889
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top