Discuss Loop Impedance tester electrical circuit in the Electrical Engineering Chat area at ElectriciansForums.net

marcuswareham

Esteemed
Arms
Reaction score
199
Hi

A quick one I was wondering if anyone knows how a multifunction tester performs a loop impedance test.

I understand how to perform a test and what the results of a loop impedance test give you in working out your PSCC and earth fault current. I use my Fluke multifunction tester every day at work to do just that.

I have however seen 13a plug in style socket testers which also so an earth loop impedance test (even if the results are very vague and not particularly useful). I am just wondering how these socket tester work as they are still relatively cheap so there must be some basic circuit doing the loop test

Hope that makes sense

Thanks Marcus
 
Many loop testers inject a current and measure the Volt drop on the supply to determine the impedance.
 
The plug-in testers like the Socket-and-See that do loop impedance tests actually incorporate a microcontroller that operates a current injection circuit and takes a measurement. It's just a compact, not very precise version of what is in an MFT. It would be interesting to find some patent numbers if there are any and look up the details. These days it is possible to buy and program a fully functional digital computer for less than the price of the dropper capacitor that powers it from the mains.
 
On a historical note I believe the original testers measured the neutral earth loop as that was easier and safer. However when the supply boards started multiple earthing of the neutral in the 60's that was no longer an option and the live earth loop tester was developed.
 

Reply to Loop Impedance tester electrical circuit in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
529
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
725
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
605
I'm moving a socket installed on a lighting circuit (installed by previous owner who was a professional electrician so I assume he knew what he...
Replies
7
Views
1K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock