Discuss Low Insulation Resistance readings N-E in the Commercial Electrical Advice area at ElectriciansForums.net

TheCodboy

-
Arms
Reaction score
109
Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original busbar. Feeds a section board and from the section board it feeds 4 3 phase DB's. The DBs have one feed in and then split to a separate power and lighting DB. (Schneider). R1+R2 tests all fine on feed to the section board, then sub mains. IR between L/E & L/N all good, N/E 0.01 at the DB's. Obviously TNCS is linked so i understand the low IR values there, but even with the TP&N isolators off and the incoming earth removed from the earth bar, testing from the other side of the TP&N isolator, im still getting 0.01 N/E. Where is it still linked out? As I say I'm shadowing a guy as its been a while since I've done much testing, he was confident to energize the DB's, which he did, and everything is fine. I know its probably something very simple but its driving me mad why I cant figure it out. I'm getting a lot of "thats fine dont worry" but i like to understand for myself. Hope someone can point me in the right direction. Thanks in advance
 
No, testing from the top of the rcbo's. We're also getting the same result on the MCB circuits. Its on every DB too. Im obviously missing something simple.

Unless those RCBO's are switching the neutral then you will still be testing through the electronics between the neutral and earth within the RCBO.
 
Unless those RCBO's are switching the neutral then you will still be testing through the electronics between the neutral and earth within the RCBO.
That would make sense as I'm not sure if they are switching the neutral, but why am I getting the same on the non RCD/RCBO circuits in the lighting DB?
 
That would make sense as I'm not sure if they are switching the neutral, but why am I getting the same on the non RCD/RCBO circuits in the lighting DB?

How exactly are you carrying out the tests?

If you are testing with the circuits connected to the neutral bar then it will be the same thing as the RCBO's are also connected to the neutral bar.
 
How exactly are you carrying out the tests?

If you are testing with the circuits connected to the neutral bar then it will be the same thing as the RCBO's are also connected to the neutral bar.
Yeah I'm testing the same. The 2 DB' are fed from the same feed. So if I understand you correctly,the 2 neutrals (lighting & power) are essentially the same neutral and the rcbos are probably causing this issue.
 

Reply to Low Insulation Resistance readings N-E in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
586
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
633
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
739
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock