Discuss Low Voltage on metal light fittings in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Old two core cable in a lighting circuit with no cpc at any point

All points had metal fixtures and fittings class1

At two points the live loop had been wired into the earth point of a light fitting one on the downstairs lights woth the bathroom above which when on gave a 130 volts on the metal legs of the bath and the screws in the floor boards around the bath.

When the two fittings had the loop removed from the earth terminal of the lights the voltage on the bath taps went to 0volts and the voltage on the screws on the floor dropped to 5.5volts

all the metal light fittings have a voltage on the metal casing between earth of 7 volts and below still apart from when the mcb was off

Why did it not drop to 0 volts is it due to the lack of a cpc

Cliff noted
Testing from the met to each point with a long lead

5ish volts at each metal light ( ni cpc in cable!)

5ish volts in screws in floor under bath

Volts drop to 0 when circuit off
 
Last edited:

Reply to Low Voltage on metal light fittings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
555
100 volts on a metal ceiling grid when measuring from the Met to the ceiling grid Only when lighting circuit (led panels ) is on it goes away if...
Replies
7
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
464
Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
691
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
627

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock