Hi everyone,

Happy Friday!

Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve looked in the BBB but to no avail on the Max Zs tables. I’ve also looked on our Cert software as they have a Max Zs app but the MCCB category doesn’t include Bill. I’m sure Bill is now MEM/Eaton, I just can’t tally up any MEM/Eaton MCCB’s with the one I’m looking for.

It’s the only part of my MW Cert I’ve got left to fill in.

Many thanks for any help.
 
Try contacting Eaton for the data.

Unlike MCB that have well-defined characteristics via the B/C/D-curve aspect, MCCB are a law unto themselves and some are adjustable so those setting need taken in to consideration as well.

Typically they are a bit like D-curve MCB (high magnetic trip point), but as above the only definitive answer is to get the specific model's data.
 
As far as I can tell they are the same as the memshield 2 F frame MCCBs
Bill had been taken over by MEM at that point and so their products were identical apart from the printing on the front (much like the MG/Square D situation)

This is a screenshot of the relevant page of the datasheet.

Screenshot_20230804_162235_com.google.android.apps.docs.jpg
 
Try contacting Eaton for the data.

Unlike MCB that have well-defined characteristics via the B/C/D-curve aspect, MCCB are a law unto themselves and some are adjustable so those setting need taken in to consideration as well.

Typically they are a bit like D-curve MCB (high magnetic trip point), but as above the only definitive answer is to get the specific model's data.
I will definitely contact Eaton, I did send an email to our wholesalers to see if they knew or could contact Eaton for us. Hopefully I'll have a reply come Monday/Tuesday.

The MCCB that feeds the isolator is just a standard one with just a push to trip button. All the others in the panel board have the adjustable dials ranging from 80A to 160A.

Thank you for the reply.
 
As far as I can tell they are the same as the memshield 2 F frame MCCBs
Bill had been taken over by MEM at that point and so their products were identical apart from the printing on the front (much like the MG/Square D situation)

This is a screenshot of the relevant page of the datasheet.

View attachment 109781

Thank you very much Dave! I really appreciate it.

I'm going to print those sheets and file them in our office because I'm pretty sure they'll come in handy in the future as we have two big panel boards made by Bill Talisman.

Thanks again.
 

Reply to Max Zs for Bill Talisman MCCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
0
Views
851
Hi there, Just after some advice for a submain/DB I’m quoting. A client has asked for a 12way TP board to be installed in a warehouse and the...
Replies
14
Views
4K
Im specking a large 480a cable over 160m ive done cable calcs and come up with 2x 120mm 70c armored. now Im trying to work out my max zs...with no...
Replies
6
Views
1K
Hi All Any one know what MCB's will fit the bill talisman 3 phase boards. Obviously MEM Eaton which are also a pain to get hold of. Was given a...
Replies
6
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock